We did double check that and found there was one neutral that did not get pulled out of the neutral bar. Even with that isolated it faulted.
I have a Fluke meter (my son works there and gets me all kinds of stuff) and if I know what to check I could do that.
Thanks for the advice and I will do more troubleshooting.
It seemed random as the electrician and I tried different circuits and worked to keep things balanced between the legs, but it would seem it could be a number of different circuits on the 6852 that caused it to have a ground fault. We...
I spent yesterday putting in one of these Generac 6852 with an electrician so I did it correctly. We put in a couple of tandem breakers to get to 10 circuits like I had on my previous transfer switch. But it is not working correctly while using ProPower from the truck. I don’t get the bonded...