  1. Generac 6852 Transfer Switch installed (to power my house from the Pro Power 240V plug)

    I did an intermix of Square D and Siemens. Looks a little inconsistent but that's about it.
  2. Generac 6852 Transfer Switch installed (to power my house from the Pro Power 240V plug)

    I used Square D tandem breakers and single breakers when I expanded to 10 circuits. The electrician recommended that I get these.
  3. Generac 6852 Transfer Switch installed (to power my house from the Pro Power 240V plug)

    We did double check that and found there was one neutral that did not get pulled out of the neutral bar. Even with that isolated it faulted. I have a Fluke meter (my son works there and gets me all kinds of stuff) and if I know what to check I could do that.
  4. Generac 6852 Transfer Switch installed (to power my house from the Pro Power 240V plug)

    Thanks for the advice and I will do more troubleshooting. It seemed random as the electrician and I tried different circuits and worked to keep things balanced between the legs, but it would seem it could be a number of different circuits on the 6852 that caused it to have a ground fault. We...
  5. Generac 6852 Transfer Switch installed (to power my house from the Pro Power 240V plug)

    I spent yesterday putting in one of these Generac 6852 with an electrician so I did it correctly. We put in a couple of tandem breakers to get to 10 circuits like I had on my previous transfer switch. But it is not working correctly while using ProPower from the truck. I don’t get the bonded...