Just finished installing a Mico-Air EasyStart on my 3.5-ton heat pump. It reduced the lock rotor current (in-rush current) by 75% from 85 amps down to 21 amps! This now allows the Lightning's ProPower to successfully start and run the heat pump without even a flinch. Prior to this, the 85 amp in-rush current on the heat pump would immediately trip the overload circuit breaker on the ProPower. Therefore I could not use the ProPower to run the central heat/AC. Now it runs it runs it no problem.
With ProPower running the house, I can have all my lights, electronics, refrigerator, well pump, and central heat/ac all operating normally. I turn off the 4000 watt hot water heater tank unless needed. I use a UL listed generator inlet and UL listed interlock to backfeed the panel with the main shut off.
With normal HVAC, the truck can power my whole house in normal operation for approx 2 full days with a 50 mile reserve. If the weather is nice and I don't need HVAC, that time goes up to 7 full days!