Sound right? Electrician recommended 40A with UF 8/3 outdoor wire to be buried under my concrete

bewbie

Well-known member
Joined
Apr 7, 2022
Threads
29
Messages
391
Reaction score
166
Location
NYC
Vehicles
2022 Lightning Lariat ER Rapid Red
My electrician recommended 40A with UF 8/3 outdoor wire to be buried under my concrete. Does that sound right?
Sponsored

 

jerock

Well-known member
First Name
Jerry
Joined
Apr 12, 2022
Threads
5
Messages
338
Reaction score
328
Location
Kansas
Vehicles
F150 Lightning
It would depend on the charger you plan on using. It's not adequate for the Pro Charger. It's not even adequate for the mobile charger.
 

jerock

Well-known member
First Name
Jerry
Joined
Apr 12, 2022
Threads
5
Messages
338
Reaction score
328
Location
Kansas
Vehicles
F150 Lightning
Ford recommends for the mobile charger a 14-50 outlet which requires a 50 amp circuit. 50 amp circuit which requires 6 gauge wire.
 

Stlww18

Well-known member
Joined
Apr 12, 2022
Threads
21
Messages
296
Reaction score
416
Location
St. Louis
Vehicles
2022 Lightning Pro, 6/3 blend date
It would depend on the charger you plan on using. It's not adequate for the Pro Charger. It's not even adequate for the mobile charger.
Mobile charger only pulls 32 amps max, which I’ve found curious given the 14-50 plug. I guess 14-50 is just a more common plug
 

Amps

Well-known member
Joined
Feb 21, 2022
Threads
5
Messages
1,288
Reaction score
1,415
Location
Mid-Atlantic
Vehicles
Bolt
That would work with a 40 Amp breaker and the 32 Amp Ford Mobile. That would be the maximum you could charge on that circuit with any EVSE.
 

Sponsored

PV2EV

Well-known member
Joined
Apr 17, 2022
Threads
48
Messages
660
Reaction score
451
Location
Oregon
Vehicles
2015 Chevy Volt, 2006 Kubota L39, 2006 Suzuki Eige
For a 32amp EVSE, yes. 14h hours for a full charge on an SR battery.
 

jerock

Well-known member
First Name
Jerry
Joined
Apr 12, 2022
Threads
5
Messages
338
Reaction score
328
Location
Kansas
Vehicles
F150 Lightning
Yes you are right about the 32 amp charger & a 40 amp circuit. If I was burying cables under concrete I would future proof it with more than a 40 amp circuit.

Here's the installation recommendations for the 80 amp Pro charger. I'd give this to your electrician. He should know the wiring required for each amperage of charger

https://www.ford.com/cmslibs/conten...ightning/pdf/Lightning_FCSP_Install_Specs.pdf

Here's the installation for Ford's Connected Charge Station & Mobile charger.
https://www.ford.com/ntzlibs/conten...-sheet/Home_Install_Spec_Sheet_0831_FINAL.pdf
 

krusshall

Well-known member
Joined
Jun 3, 2022
Threads
3
Messages
216
Reaction score
168
Location
Charlotte, NC area
Vehicles
2021 VW ID.4, 2022 Polestar 2, 2016 Ram 1500
Recommended 40A what? The circuit? I would do a 50A rated circuit so that you can have an EVSE rated up to 40A. 8 gauge copper wire ampacity is sufficient and three conductors are needed - two hots and a ground for 240 V.
 

Stlww18

Well-known member
Joined
Apr 12, 2022
Threads
21
Messages
296
Reaction score
416
Location
St. Louis
Vehicles
2022 Lightning Pro, 6/3 blend date
That would work with a 40 Amp breaker and the 32 Amp Ford Mobile. That would be the maximum you could charge on that circuit with any EVSE.
Only issue I see is you can either get a 14-30 or a 14-50 receptacle. No such thing as a 14-40. Even with a 40 amp breaker and a 40 am (32 actual) evse, by code you couldn’t put a 14-50 plug on it
 

PV2EV

Well-known member
Joined
Apr 17, 2022
Threads
48
Messages
660
Reaction score
451
Location
Oregon
Vehicles
2015 Chevy Volt, 2006 Kubota L39, 2006 Suzuki Eige
You would be better served/future proofed by going 6-3 UF-B for a 48amp EVSE. That is 10 hours for an SR.
 

Sponsored

VTbuckeye

Well-known member
First Name
Joseph
Joined
Jan 15, 2022
Threads
3
Messages
854
Reaction score
820
Location
Vermont
Vehicles
19 Bolt, 16 XC90T8, 22 XC40 P8 Recharge, 17 Tacoma
The 14-50 outlet with 8x3 wiring will work for a 30 amp evse, but not for a 40 amp evse. The 14-50 outlet is supposed to be a 50 amp capable outlet and it would be unsafe to only wire it to be 40 amp capable. 14-50 needs to be wired with 6 guage wire to be safe and proper.
 
OP
OP

bewbie

Well-known member
Joined
Apr 7, 2022
Threads
29
Messages
391
Reaction score
166
Location
NYC
Vehicles
2022 Lightning Lariat ER Rapid Red
it would just be for an ev in general not the f150
 

Amps

Well-known member
Joined
Feb 21, 2022
Threads
5
Messages
1,288
Reaction score
1,415
Location
Mid-Atlantic
Vehicles
Bolt
The 14-50 outlet with 8x3 wiring will work for a 30 amp evse, but not for a 40 amp evse. The 14-50 outlet is supposed to be a 50 amp capable outlet and it would be unsafe to only wire it to be 40 amp capable. 14-50 needs to be wired with 6 guage wire to be safe and proper.
I'm not sure why you think that would be unsafe. I agree that it's not ideal.

You can protect a 14-50R with a 40 Amp breaker. Table 210.24:

https://up.codes/s/branch-circuit-requirements-summary
 

Amps

Well-known member
Joined
Feb 21, 2022
Threads
5
Messages
1,288
Reaction score
1,415
Location
Mid-Atlantic
Vehicles
Bolt
it would just be for an ev in general not the f150
Your electrician is trying to save you money on the cable costs. Others have suggested that you spend a bit more money to future proof it. The electrician has limited you to 32 Amp charging maximum.
 

besch2410

Member
First Name
Ryan
Joined
Mar 3, 2022
Threads
1
Messages
19
Reaction score
38
Location
Johnson City, TN
Vehicles
F150 Lightning
I'm going to make the mistake of assuming that this sub-concrete run involves conduit. I'd actually tell you to consider oversizing the conduit, that way of you decide to upgrade to a larger charger (or add a second), the conduit is large enough to meet code. The 40A breaker and 8-gauge is fine. Putting a 50A plug on a 40A circuit is not a problem. The problem would be a hypothetical 40A plug on a 50A circuit (due to excess resistance and heat in the plug if fully loaded).