It does require some hard thinking though.I think you are over thinking this. The GFCI only trips if the current leaving the Lightning on the hot wires doesn't equal the current coming back on the neutral wire. If the ground wire is connected, then it is the only other path; so if the GFCI trips there is source current coming back on the ground wire. Current can only come back on the ground wire if there some connection between it and the source (Lightning) hot wires or source neutral wire. The secondary side of an isolation xfmr is a separate circuit all together, unless it's faulty, which is unlikely.
Well in theory the isolation transformer is perfectly isolated.
But we have to consider the reality - that real transformers (even isolation transformers) have some, maybe small but not zero, capacitance between their primary and secondary, and that capacitance can pass AC. Not DC of course unless there is an electrical short.
Yes you need a complete circuit, and the ground along with the capacitance of the transformer could provide that.
Even if there is no neutral connection to the transformer primary, the neutral in the Lightning is still connected to ground. So is the center tapped secondary grounded neutral of the transformer.
Any difference is voltage between the grounded center tapped neutral of the secondary and the grounded neutral in the Lightning could cause a ground current to flow the capacitance of the transformer windings completing the circuit.
How much current would flow?
A small amount but...how much does it take to pop the GFCI?
Not much.
Just saying it is a possibility.
Without a grounded center tap (or other wire) neutral on the transformer secondary, it would be a real isolation transformer implementation and no tripping should occur. But then it would not comply with the code which requires a grounded neutral.
If you ground any secondary conductor of an isolation transformer, you eliminate the "isolation" that is canonical.