i'm sure this has been previously discussed but need a quick answer.

while i wait for sun run, i can't just plug in the 30A mobile charger into a standard outlet in garage, right? because standard outlets are 15A or 20A?

sorry, i did a quick search already.
Sponsored

 

Pioneer74

Well-known member
Joined
Aug 16, 2021
Threads
38
Messages
3,819
Reaction score
6,973
Location
Dearborn
Vehicles
2022 Lightning Lariat ER - 2025 Mach-E Premium ER
Occupation
Electrician
You can plug it into a standard outlet. It will draw about 12 amps. You won't be using the changeable plug that uses the NEMA 14-50 socket. You won't gain range very fast, but it will charge.
 

2wheeltraveler

Well-known member
Joined
Oct 4, 2021
Threads
22
Messages
141
Reaction score
199
Location
Austin, TX
Vehicles
2022 F150 Lightning Lariat Rapid Red
that sounds terrible when you put it like that but then again that should maintain many folks for most days.
It’s adding enough to get to and from work each day and when we got too low we made a quick trip to the nearest 150KW charger to top off. Totally manageable considering we’ve put 500 miles on it in 3 days…
 

Sponsored

Firestop

Well-known member
First Name
Firestop
Joined
May 6, 2022
Threads
13
Messages
1,033
Reaction score
1,005
Location
Oregon
Vehicles
2022 F-150 L Lariat ER; Honda Accord Touring
that sounds terrible when you put it like that but then again that should maintain many folks for most days.
Yes, yes it is terrible…my truck is on 120V/20A now…limping along until I get my FCSP delivered/installed/derated (until Siemens solves their issues). I’m averaging adding about 1.0 kWhr per hour of charge time……
Ford F-150 Lightning mobile charger with garage outlet 9C23276D-8BA2-455C-B6DF-AB4CB920CF05
 

Lightning.Dav

Well-known member
First Name
David
Joined
Jun 2, 2021
Threads
5
Messages
152
Reaction score
158
Location
Temecula, CA
Vehicles
Sienna x 2
I don't have the FCSP yet, but I had an electrician come out and run the #3 copper wire to where I want the FCSP installed.

As long as he was here anyway, I had him put in a 240v 50amp 14-50 so I can use that until I get the FCSP and have it connected.
 

Yellow Buddy

Well-known member
Joined
Feb 5, 2022
Threads
27
Messages
2,511
Reaction score
3,371
Location
Mid-Atlantic
Vehicles
F-150L Pro, Rivian R1T, Model S, Model X
Occupation
Smart Ass
i'm sure this has been previously discussed but need a quick answer.

while i wait for sun run, i can't just plug in the 30A mobile charger into a standard outlet in garage, right? because standard outlets are 15A or 20A?

sorry, i did a quick search already.
You can plug it in. It’ll take you over a week to charge from empty to full. Only viable if you drive once a week.

If you have an electric drier that’s close to where you can get the truck, the dryer plug can be used and will do much better.
 

RickLightning

Well-known member
Joined
Jan 17, 2022
Threads
107
Messages
6,822
Reaction score
9,302
Location
SE MI
Vehicles
'22 Lightning ER Lariat,'22 Mach-E Premium 4X
Yes, yes it is terrible…my truck is on 120V/20A now…limping along until I get my FCSP delivered/installed/derated (until Siemens solves their issues). I’m averaging adding about 1.0 kWhr per hour of charge time……
Correct. 1 kWh per hour on 120v.

You can plug it in. It’ll take you over a week to charge from empty to full. Only viable if you drive once a week.

If you have an electric drier that’s close to where you can get the truck, the dryer plug can be used and will do much better.
dryer

No, do not do this. The Ford Mobile Charger pulls 30 amps. That requires the wiring and breaker for a 40amp circuit. 30amp dryer wiring is not adequate.
 
Last edited:

Yellow Buddy

Well-known member
Joined
Feb 5, 2022
Threads
27
Messages
2,511
Reaction score
3,371
Location
Mid-Atlantic
Vehicles
F-150L Pro, Rivian R1T, Model S, Model X
Occupation
Smart Ass
dryer

No, do not do this. The Ford Mobile Charger pulls 30 amps. That requires the wiring and breaker for a 40amp circuit. 30amp dryer wiring is not adequate.
Is the F150L not amperage selectable like the Tesla?
 

Sponsored

RickLightning

Well-known member
Joined
Jan 17, 2022
Threads
107
Messages
6,822
Reaction score
9,302
Location
SE MI
Vehicles
'22 Lightning ER Lariat,'22 Mach-E Premium 4X

FlasherZ

Well-known member
Joined
Mar 10, 2022
Threads
9
Messages
915
Reaction score
1,027
Location
St. Louis Metro
Vehicles
F-150 Lightning, Tesla Model X, F250 SD diesel 6.0
That is what the 30amp breaker is for right? Its been a minute but doesnt the gauge wire for a 30 amp circuit the NEC calls for provide enough for 32 or 33amps? In either case I would be surprised if the F150 Lightning doesnt do a sense probe with a draw ramp.

Once my truck gets here ill do a test for this, I can monitor temp, volts, amps and some other parameters for my house wiring.
No.

The NEC says that your circuit must be sized for 125% of the charging current because it is classified as a continuous load (it does not cycle on and off like many other loads do). This means that for a 30A EV charging load, you require a minimum circuit ampacity of 37.5A - so you round up to 40A. You are not permitted to draw 30A EV charging load from a conductor rated for 30A.

The F-150 (nor any other EV, really) does not do a sense probe. It draws what the EVSE tells it is available, and it's not adjustable in the truck. And the Ford mobile charger with a NEMA 14-50 plug advertises 30A charging load to the truck.

Tesla (and other EV's) do have sense for potential high resistance problems (significant voltage drop indicative of an undersized circuit or an extension code) and will cut their current draw based on that. I'm not sure how much Ford looks for this or not.
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
4,301
Reaction score
5,751
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
No.

The NEC says that your circuit must be sized for 125% of the charging current because it is classified as a continuous load (it does not cycle on and off like many other loads do). This means that for a 30A EV charging load, you require a minimum circuit ampacity of 37.5A - so you round up to 40A. You are not permitted to draw 30A EV charging load from a conductor rated for 30A.

The F-150 (nor any other EV, really) does not do a sense probe. It draws what the EVSE tells it is available, and it's not adjustable in the truck. And the Ford mobile charger with a NEMA 14-50 plug advertises 30A charging load to the truck.

Tesla (and other EV's) do have sense for potential high resistance problems (significant voltage drop indicative of an undersized circuit or an extension code) and will cut their current draw based on that. I'm not sure how much Ford looks for this or not.
Instructions with the Ford Mobile Charger indicate that the temperature, both internally and at the supply plug, is monitored and the output throttled if an over temp condition is detected. This causes the dreaded amber light, reduced output reported by quite a few people. I don’t find anything to indicate that voltage drop is monitored, but I found it interesting that the 14-50P temperature is.
Sponsored

 
 