I am working on Innovating with the Ford Home Integration system. I have included a rudimentary diagram showing the parts of the system and how power flows through the system in both modes - charging the F150 (Grid On) and discharging to home AC load (Grid Off). My diagram is a work in progress. it is based on the wiring diagrams in the Ford Home Integration System Installation and Wiring document.

My diagram: https://www.f150lightningforum.com/forum/attachments/f2-pdf.71941/

I have one question that is not obvious to me from that diagram. By what mechanism is the Dark Start battery charged?
Sponsored

 

Attachments

djwildstar

Well-known member
First Name
Guy
Joined
Mar 14, 2023
Threads
2
Messages
170
Reaction score
216
Location
Atlanta, GA
Vehicles
2023 Lightning Lariat ER, 2023 Mach-E GTPE
Occupation
Information Security
NealG,

Looking good! With respect to your diagram:
  • What you label as "Grid" is the main service panel and associated equipment.
    • At minimum, this should show the meter, main breaker, and breakers for the FCSP (EVSE) and non-critical loads.
    • An Acrel current meter is used to sense current on the main feeder lines via current transducers (CT) installed on those lines. The sense lines from the CTs to the Acrel Meter are not RS485 -- these are analog sense lines between the meter and its current transducers.
  • The connections to the transfer switch (WHB/MID or Whole Home Backup / Microgrid Interconnect Device in SunRun's documentation) don't seem correct. Specifically:
    • There is no connection from the dark-start battery to the WHB/MID.
      • As far as I can tell, the WHB/MID doesn't need power to switch from grid power to backup power -- this happens automatically when grid power fails.
      • I'm guessing that the WHB/MID does need grid power ON as well as confirmation from the BDI (inverter) that either backup power is OFF or that solar production is synchronized with the grid before it reconnects the load to grid power.
    • There is an RS485 connection from the WHB/MID to the BDI (inverter), which would supply this confirmation signal.
  • The connections to the inverter (BDI or Bi-Directional Inverter in SunRun's documentation) also don't seem complete.
    • There are RS485 connections:
      • From the BDI to the WHB/MID
      • From the BDI to the FCSP (Ford Charge Station Pro or EVSE)
    • There is a 12V connection from the BDI to the FCSP.
      • This supplies the FCSP with power from the dark-start battery so that the FCSP and BDI can communicate with the truck and bring backup power online.
      • It appears that the BDI manages the dark-start battery, potentially including supplying charging current to the battery when needed.
    • In SunRun solar setups, the solar array and optional stand-alone backup battery also connect to the BDI.
 

v2h8484

Well-known member
Joined
Mar 3, 2023
Threads
3
Messages
132
Reaction score
59
Location
USA
Vehicles
Tesla Model 3
I have one question that is not obvious to me from that diagram. By what mechanism is the Dark Start battery charged?
Most likely there is a small charger that charges the 12V dark start battery whenever DC power from the truck is enabled. It's similar to how the 12V battery gets charged in cars and generators with electric start.
 

Jim Lewis

Well-known member
First Name
Jim
Joined
Jan 10, 2023
Threads
39
Messages
715
Reaction score
585
Location
San Antonio, TX
Vehicles
Honda Accord 2017; 2023 Lariat ER
Occupation
Retired

Wattsgas

Active member
First Name
MIke
Joined
Jan 8, 2022
Threads
3
Messages
41
Reaction score
50
Location
Brinnon, WA
Vehicles
22 Lightning Platinum, Ford F250, Rivian R1S
There is also a communication line from the charger to the inverter.
 

Sponsored
OP
OP

NealG

Member
First Name
Neal
Joined
Jul 17, 2023
Threads
2
Messages
6
Reaction score
3
Location
Hamden, CT
Vehicles
Prius
Occupation
Project Manager
NealG,

Looking good! With respect to your diagram:
  • What you label as "Grid" is the main service panel and associated equipment.
    • At minimum, this should show the meter, main breaker, and breakers for the FCSP (EVSE) and non-critical loads.
    • An Acrel current meter is used to sense current on the main feeder lines via current transducers (CT) installed on those lines. The sense lines from the CTs to the Acrel Meter are not RS485 -- these are analog sense lines between the meter and its current transducers.
  • The connections to the transfer switch (WHB/MID or Whole Home Backup / Microgrid Interconnect Device in SunRun's documentation) don't seem correct. Specifically:
    • There is no connectionfrom the dark-start battery to the WHB/MID.
      • As far as I can tell, the WHB/MID doesn't need power to switch from grid power to backup power -- this happens automatically when grid power fails.
      • I'm guessing that the WHB/MID does need grid power ON as well as confirmation from the BDI (inverter) that either backup power is OFF or that solar production is synchronized with the grid before it reconnects the load to grid power.
    • There is an RS485 connection from the WHB/MID to the BDI (inverter), which would supply this confirmation signal.
  • The connections to the inverter (BDI or Bi-Directional Inverter in SunRun's documentation) also don't seem complete.
    • There are RS485 connections:
      • From the BDI to the WHB/MID
      • From the BDI to the FCSP (Ford Charge Station Pro or EVSE)
    • There is a 12V connection from the BDI to the FCSP.
      • This supplies the FCSP with power from the dark-start battery so that the FCSP and BDI can communicate with the truck and bring backup power online.
      • It appears that the BDI manages the dark-start battery, potentially including supplying charging current to the battery when needed.
    • In SunRun solar setups, the solar array and optional stand-alone backup battery also connect to the BDI.
Thanks for your input, I am going to revise the diagram and repost it here when I figure more things out. Thanks to the other posters for their input.
 
OP
OP

NealG

Member
First Name
Neal
Joined
Jul 17, 2023
Threads
2
Messages
6
Reaction score
3
Location
Hamden, CT
Vehicles
Prius
Occupation
Project Manager
I have also gotten useful information from Sunrun field support. They say the DS Battery is charged during Grid On time from the BDI. which leads me to wonder where the BDI is getting that energy from. It's not clear to me from the diagram.
 

djwildstar

Well-known member
First Name
Guy
Joined
Mar 14, 2023
Threads
2
Messages
170
Reaction score
216
Location
Atlanta, GA
Vehicles
2023 Lightning Lariat ER, 2023 Mach-E GTPE
Occupation
Information Security
I have also gotten useful information from Sunrun field support. They say the DS Battery is charged during Grid On time from the BDI. which leads me to wonder where the BDI is getting that energy from. It's not clear to me from the diagram.
It looks like the BDI gets power from the backup subpanel when grid power is on. In particular: The RSD AC Disconnect labels the side of the disconnect switch that connects to the backup subpanel as "Line" and the side that connects to the BDI as "Load". Similarly, the AC terminals of the BDI are labelled AC IN in the SunRun system wiring diagram.

This suggests that during normal operation the BDI's AC IN terminals are in fact inputs, and the BDI uses that power to run itself, and charge the dark start battery. When grid power is out, the bidirectional inverter reverses this, and outputs power on the AC IN terminals.
 
  • Like
Reactions: chl

chl

Well-known member
First Name
CHRIS
Joined
Dec 16, 2022
Threads
5
Messages
669
Reaction score
345
Location
alexandria virginia
Vehicles
2001 FORD RANGER, 2023 F-150 LIGHTNING
It looks to me like the BID is getting grid power to keep the dark start battery charged from the main service panel "feeder breaker" that feeds AC to the "backup sub-panel" through the MID as I boxed in red in the circuit diagram:

Ford F-150 Lightning Basic understanding of HIS (Home Integration System) functionality Integration System CSP-SunRun wiring 2


Not shown is a block diagram of the BID insides where there must be a AC-DC converter to keep the 12v dark start battery topped off.

The Block Diagram below confirms the BID gets grid power when the grid is up.

Ford F-150 Lightning Basic understanding of HIS (Home Integration System) functionality Grid Power On diagram


Ford F-150 Lightning Basic understanding of HIS (Home Integration System) functionality Grid Power Off diagram
 

rraustad

Active member
First Name
Richard
Joined
Aug 20, 2023
Threads
0
Messages
39
Reaction score
46
Location
Florida
Vehicles
2023 F150 Lightning XLT SR
Does this mean that only the home owner's vehicle can use the HIS to power the home? I am curious if any F150L can pull up to this HIS, plug in, and power the home during a power outage? For example, if this HIS was installed on a community center, or homeless shelter, could any F150L pull up and help power the building? I am curious if the HIS is specific to a certain truck (somehow paired where other F150Ls would not work).

Ford F-150 Lightning Basic understanding of HIS (Home Integration System) functionality 1724455655469-tl
 

Sponsored

tearitupsports

Active member
First Name
Russell
Joined
Jun 1, 2024
Threads
4
Messages
35
Reaction score
27
Location
Houston, TX
Vehicles
F-150 Lightning Lariat ER
Does this mean that only the home owner's vehicle can use the HIS to power the home? I am curious if any F150L can pull up to this HIS, plug in, and power the home during a power outage? For example, if this HIS was installed on a community center, or homeless shelter, could any F150L pull up and help power the building? I am curious if the HIS is specific to a certain truck (somehow paired where other F150Ls would not work).

1724455655469-tl.png
It’s a great question. I will try it in a few weeks hopefully.
 

Jim Lewis

Well-known member
First Name
Jim
Joined
Jan 10, 2023
Threads
39
Messages
715
Reaction score
585
Location
San Antonio, TX
Vehicles
Honda Accord 2017; 2023 Lariat ER
Occupation
Retired
I am curious if the HIS is specific to a certain truck (somehow paired where other F150Ls would not work).
Yes, your truck must be BT-paired to the FCSP to provide backup power. AFAIK the reason being that the FCSP lets the truck know through BT that there is no grid power and it's OK to initiate backup power transfer. In past forum discussions, the poor BT connectivity between truck and FCSP has been cited by forum members as a reason for the failure of backup power transfer, with advice to park the truck with the right rear passenger seat as close to the FCSP as possible to facilitate the BT communication needed to enable power transfer. The truck's BT module is behind the right rear passenger seat, whereas the FCSP is typically positioned on the left side of the truck, as that's where the charging port is located ( 🙄). Poor BT communication = failed power transfer.
 
Last edited:

rraustad

Active member
First Name
Richard
Joined
Aug 20, 2023
Threads
0
Messages
39
Reaction score
46
Location
Florida
Vehicles
2023 F150 Lightning XLT SR
OK, so let's assume that a blue tooth pairing is required. Couldn't any F150 pull up , pair with the system, and just get started?, is the initial pairing a show stopper?