I;m not sure how you think that would be unsafe.

You can protect a 14-50R with a 40 Amp breaker. Table 210.24:

https://up.codes/s/branch-circuit-requirements-summary
Thanks for correcting me. When I see a 14-50 outlet I assume 50amp construction and capability. As long as the wiring and breaker match then it will be safe. It could be inconvenient if one were to draw 40+ amps on the circuit and the breaker trips shutting down the circuit.
Sponsored

 

Tony Burgh

Well-known member
First Name
Tony
Joined
Sep 28, 2021
Threads
23
Messages
966
Reaction score
1,195
Location
Western Pennsylvania
Vehicles
22 Lariat ER
Occupation
Retired
NEC/NFPA requires the circuit breaker be 25% greater than the evse output amperage. Wire should be sized for circuit breaker rating.
As the home owner you can do what you want and hope nothing happens. A licensed electrician must follow applicable codes.
 

Beans

Well-known member
First Name
Phil
Joined
Jan 7, 2022
Threads
4
Messages
159
Reaction score
216
Location
Beaver Dam, WI
Vehicles
Acura RDX, Toyota 4 Runner
I’m not an electrician, but from research I believe code requires conduit at least 18 inches below the surface For 240v power.
 
OP
OP

bewbie

Well-known member
Joined
Apr 7, 2022
Threads
31
Messages
409
Reaction score
174
Location
NYC
Vehicles
2022 Lightning Lariat ER Rapid Red
I was told the outdoor wire would not require conduit. Also, this is for my father who will be getting an ev in the future, my f150 will have the pro charger in the garage next to panel. I am just curious since we are trying to plan for the future, what would be the best setup for my fathers future ev?
 

PV2EV

Well-known member
Joined
Apr 17, 2022
Threads
53
Messages
691
Reaction score
478
Location
Oregon
Vehicles
2015 Chevy Volt, 2006 Kubota L39, 2006 Suzuki Eige
UF-B Is direct burial (no conduit), so upgrading to 6-3 would not require larger conduit, or much more cost if distance is not too much. I would do 6-3, 70 amp breaker and 14-50 outlet.
 

Sponsored

Amps

Well-known member
Joined
Feb 21, 2022
Threads
5
Messages
1,336
Reaction score
1,518
Location
Mid-Atlantic
Vehicles
Bolt
I am just curious since we are trying to plan for the future, what would be the best setup for my fathers future ev?
IMHO, the sweet spot is up-sizing the conductors to #6, install a 14-50R for 40 Amp charging (50 Amp breaker), leaving yourself enough cable to possibly hard-wire an EVSE in for a maximum 48 Amp charging (60 Amp breaker). That means for the increased price of the wire, you get 125% more capability with a receptacle and 150% more capability if you hard-wire, above the 32 Amp maximum you've been quoted.

The caveat is that the entire project conform to code and be inspected, if required.
 

FlasherZ

Well-known member
Joined
Mar 10, 2022
Threads
9
Messages
915
Reaction score
1,025
Location
St. Louis Metro
Vehicles
F-150 Lightning, Tesla Model X, F250 SD diesel 6.0
It is legal to install a NEMA 14-50 receptacle with a 40A breaker *IF* the load is designed for it (e.g., if your EVSE can charge at 40A, you're not allowed to do that). 8/3 UF-B cable is good to 40A capacity (because you must use the 60 degC column of ampacity), which is only good for 32A charging because of the 125% capacity for continuous load requirements. You may NOT put a 50A breaker on that installation. That will work for Tesla or Ford mobile chargers that do charging at 32A.

Given that many EV's are targeting 48A charging (60A capacity), if you're doing burial work, I'd bury a conduit and put in #6 THWN. That has 65A capacity on the wires and gives you the most flexibility balanced with lower cost.

Of course, the best flexibility would be to get you a 100A or 125A feeder to your outbuilding, but at some point it gets to be a cost trade-off.

There are also some limitations if you are running this circuit to an existing outbuilding that already has a power feeder to it. Your electrician can help you with the right solution.
 

Sponsored

FlasherZ

Well-known member
Joined
Mar 10, 2022
Threads
9
Messages
915
Reaction score
1,025
Location
St. Louis Metro
Vehicles
F-150 Lightning, Tesla Model X, F250 SD diesel 6.0
if its 240v wouldnt i just need 2 hots and a ground? what would be the purpose of having 4 wires?
NEMA 14 series receptacles require a neutral. Never connect a NEMA 14 receptacle with no neutral, and never tie ground to neutral at that receptacle (or you'll find weird ground paths flow through that receptacle).

NEMA 6 series is 2 hots + ground, but EV manufacturers settled on 14-series because of its use with RV's.
 
OP
OP

bewbie

Well-known member
Joined
Apr 7, 2022
Threads
31
Messages
409
Reaction score
174
Location
NYC
Vehicles
2022 Lightning Lariat ER Rapid Red
It is legal to install a NEMA 14-50 receptacle with a 40A breaker *IF* the load is designed for it (e.g., if your EVSE can charge at 40A, you're not allowed to do that). 8/3 UF-B cable is good to 40A capacity (because you must use the 60 degC column of ampacity), which is only good for 32A charging because of the 125% capacity for continuous load requirements. You may NOT put a 50A breaker on that installation. That will work for Tesla or Ford mobile chargers that do charging at 32A.

Given that many EV's are targeting 48A charging (60A capacity), if you're doing burial work, I'd bury a conduit and put in #6 THWN. That has 65A capacity on the wires and gives you the most flexibility balanced with lower cost.

Of course, the best flexibility would be to get you a 100A or 125A feeder to your outbuilding, but at some point it gets to be a cost trade-off.

There are also some limitations if you are running this circuit to an existing outbuilding that already has a power feeder to it. Your electrician can help you with the right solution.
https://www.globalindustrial.com/p/uf-b-underground-feeder-cable-6-3-awg?ref=5

would this wire work without running conduit?
 

FlasherZ

Well-known member
Joined
Mar 10, 2022
Threads
9
Messages
915
Reaction score
1,025
Location
St. Louis Metro
Vehicles
F-150 Lightning, Tesla Model X, F250 SD diesel 6.0
UF-B Is direct burial (no conduit), so upgrading to 6-3 would not require larger conduit, or much more cost if distance is not too much. I would do 6-3, 70 amp breaker and 14-50 outlet.
You may not use a 70A breaker on either a NEMA 14-50 receptacle (50A breaker max) or UF 6-3 conductors. When you use NM cable or UF cable, you must use the 60 degC column for ampacity, and for #6 cable that's only 55A. However, because a 14-50 receptacle is maximum 50A, you may not use more than a 50A breaker to protect it.

The way the NEC works is that it starts with the load. If the load is 55A (after figuring for continuous load requirements or if not required), you select the conductor for the load to be carried (in this case, UF 6/3 would be sufficient), then select the OCPD (breaker) to protect the circuit. Because there is no 55A breaker, a 60A breaker is sufficient.
 

FlasherZ

Well-known member
Joined
Mar 10, 2022
Threads
9
Messages
915
Reaction score
1,025
Location
St. Louis Metro
Vehicles
F-150 Lightning, Tesla Model X, F250 SD diesel 6.0
OP
OP

bewbie

Well-known member
Joined
Apr 7, 2022
Threads
31
Messages
409
Reaction score
174
Location
NYC
Vehicles
2022 Lightning Lariat ER Rapid Red
That would work for a maximum of 44A EV charging (55A capacity divided by 1.25 continuous load factor). You would not be able to use that cable with an EVSE that charges a vehicle at 48A. It will work just fine for a NEMA 14-50 receptacle on the end of it with a 50A breaker for 40A EV charging.
so what would be needed for an EVSE charger at 48A?