- First Name
- CHRIS
- Dec 16, 2022
- alexandria virginia
- 2023 F-150 LIGHTNING, 2012 Nissan Leaf, 2015 Toyota Prius, 2000 HD 883 Sportster
- Occupation
- Patent Atty / Electrical Engineer
It looks like a 240VAC 30A transformer (7.2kVA) would cost in the neighborhood of $1700 and up, and would have to be wired to the house as well.Indeed but this number ignores the time, either your own experienced time or an expensive electrician, to route circuits from the main breaker to the transfer switch breaker. I had thought the isolation transformer was a good solution, if it does whole house, because it would skip that re-wiring and be cheaper than more expensive transfer switch after you added man-hours.
But all of this is moot for me, I already have the transfer switch, yet it doesn't handle the pump, so I shall get the transformer installed and be happy with everything working.
I think my electrician was a little scared of this new idea and went a little overboard on the hardware but it worked out in the end (minus the well pump).
Wiring a transfer switch like the GENERAC 6853 should not cost too much.
Yes, it looks like you have a big Seimens disconnect/transfer switch and a whole separate breaker box too. Definitely on the expensive side compared to a GENERAC 6853 install.
Although the GENERAC manual is a bit obtusely written, basically the wiring is take the hots and neutrals from the circuits you want to back up and connect them to the corresponding hots and neutral prewired in the transfer switch. You also install a 50A breaker in your main service panel and power to the transfer switch when the utility is on (to power the backed up circuits from the utility).