I still think the isolation transformer would be cheaper. You left out all the breakers you must buy and add to the Generac box, I thought those are like $50 each. Plus that time fishing wire around breaker boxes is not free. The isolation transformer Maquis linked was $700 and I presume the install is much simpler as well as implicitly power the whole panel.It looks like a 240VAC 30A transformer (7.2kVA) would cost in the neighborhood of $1700 and up, and would have to be wired to the house as well.
Wiring a transfer switch like the GENERAC 6853 should not cost too much.
Yes, it looks like you have a big Seimens disconnect/transfer switch and a whole separate breaker box too. Definitely on the expensive side compared to a GENERAC 6853 install.
Although the GENERAC manual is a bit obtusely written, basically the wiring is take the hots and neutrals from the circuits you want to back up and connect them to the corresponding hots and neutral prewired in the transfer switch. You also install a 50A breaker in your main service panel and power to the transfer switch when the utility is on (to power the backed up circuits from the utility).
The only downside I'm seeing to the isolation transformer is the power loss people talk about but I have no idea what that loss is in practice.