The neutral is connected, the ground from the main panel is not. All current on the hot legs is returning to the earth via the main panel
Current does not “return to earth.”
Sponsored

 
OP
OP
Danface

Danface

Well-known member
First Name
Dan
Joined
Sep 19, 2023
Threads
4
Messages
898
Reaction score
912
Location
Central Mass
Vehicles
2023 Lightning XLT
I posted the drawing in post #101 to show the shock hazard should the neutral connection become disconnected (failed) from an ungrounded power source.

The attached photo shows an L14-30 plug which went open due to rough handling. Although this failure was on a line connection, the open circuit could have just as easily been on the neutral pin. Prior work experience, and this failure prompted my "Show some love to your L-14 Plugs" post on this forum.

Steve

IMG_0347.jpg
100% agree. I mis-spoke, I said Nuetral but mean Ground. Inspector is coming this morning!
 
OP
OP
Danface

Danface

Well-known member
First Name
Dan
Joined
Sep 19, 2023
Threads
4
Messages
898
Reaction score
912
Location
Central Mass
Vehicles
2023 Lightning XLT
I'm not not home but the inspector came and I don' think he even looked at the charge setup so "all good"
 

FloridaMan655321

Well-known member
Joined
Jul 7, 2024
Threads
24
Messages
406
Reaction score
474
Location
Florida
Vehicles
1973 F100, 2024 Flash
Wherever it goes, it uses the neutral to get there :)
This is my thought, which leads me to believe it's a very very extreme circumstance where you would actually get shocked. Almost like you would need to design a way or create a physical cut into the wire. Again, I'm dumb, so.....
 

Sponsored
OP
OP
Danface

Danface

Well-known member
First Name
Dan
Joined
Sep 19, 2023
Threads
4
Messages
898
Reaction score
912
Location
Central Mass
Vehicles
2023 Lightning XLT
The truck has GFCI built in and the metal body and cover of the generator plug is connected to it so that would trip if that grounded out (covered with snow or something metal leaning against it) and that seems like it would be all that's needed since it would only have current to it when plugged into the truck. Now if I ever used a non GFCI generator the yes, attach the ground from the house to the generator plug box.
 

drewfaulk

Active member
Joined
Sep 27, 2022
Threads
3
Messages
43
Reaction score
18
Location
Atlanta
Vehicles
2022 F-150 Lightning
Long story short (pun intended), the GFCI on the truck will trip off if the receptical ground wire is connected to the ground wire coming from the panel. So run all 4 wires from the panel to the generator plug and don't connect the green and connect the green from the truck side of the plug to the front of the plug and to the receptical hosing.

Because the generator (truck) is not connected permanently (ie for emegency use), it's legal (in a lot of states) for the ground to float.

One NOTE, I have one more thing to do before we call the inspector but the work was done with a permit and by a licensed electrician.

1727267107829-nn.jpg
Quick question about this. Couldn't you add an additional layer of safety by capping the "ground from truck" and tying the "ground from panel" to the point where you had the truck grounded (please see below picture for reference)? It would seem that if one of the hots came out of the back of your inlet and touched the box that it would be more likely to trip the breaker, rather than energize the metal box, if the box was tied to the incoming ground (in the event someone steps on/pulls the cord, bumps the box with the car, lawnmower, hand truck, etc., uses the inlet box as a step to reach something overhead....). I imagine there's a chance the truck wouldn't like this, but it seems like I've read about people modifying cords to not have a ground, so I'd think this would work. It's always possible I'm just wrong and this doesn't do anything safety-wise....

Proposed Modification:

Ford F-150 Lightning Working Pro Power using Generator Lockout Kit to Feed the Whole Panel IMG_20240925_080549.MEDIUM
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
4,002
Reaction score
5,230
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
Quick question about this. Couldn't you add an additional layer of safety by capping the "ground from truck" and tying the "ground from panel" to the point where you had the truck grounded (please see below picture for reference)? It would seem that if one of the hots came out of the back of your inlet and touched the box that it would be more likely to trip the breaker, rather than energize the metal box, if the box was tied to the incoming ground (in the event someone steps on/pulls the cord, bumps the box with the car, lawnmower, hand truck, etc., uses the inlet box as a step to reach something overhead....). I imagine there's a chance the truck wouldn't like this, but it seems like I've read about people modifying cords to not have a ground, so I'd think this would work. It's always possible I'm just wrong and this doesn't do anything safety-wise....

Proposed Modification:

IMG_20240925_080549.MEDIUM.jpeg
It really doesn’t matter. If a live wire were to contact the box, the GFCI will trip. It will never be energized.
 

drewfaulk

Active member
Joined
Sep 27, 2022
Threads
3
Messages
43
Reaction score
18
Location
Atlanta
Vehicles
2022 F-150 Lightning
It really doesn’t matter. If a live wire were to contact the box, the GFCI will trip. It will never be energized.
That makes sense. I guess, unlike an outlet, an inlet is not energized when not in use, and, because of the interlock, would never be receiving power from the utility.
 
OP
OP
Danface

Danface

Well-known member
First Name
Dan
Joined
Sep 19, 2023
Threads
4
Messages
898
Reaction score
912
Location
Central Mass
Vehicles
2023 Lightning XLT
That makes sense. I guess, unlike an outlet, an inlet is not energized when not in use, and, because of the interlock, would never be receiving power from the utility.
That crossed my mind too and, as mentioned above, the box is GFCI protected by the truck when enegized so "toss a coin" so to speak. I guess if a circuit was leaking current to ground and/or the panel ground had a high impedence for some reason then having the panel ground isolated could prevent the input plug body from being hot maybe??
 

Sponsored

drewfaulk

Active member
Joined
Sep 27, 2022
Threads
3
Messages
43
Reaction score
18
Location
Atlanta
Vehicles
2022 F-150 Lightning
That crossed my mind too and, as mentioned above, the box is GFCI protected by the truck when enegized so "toss a coin" so to speak. I guess if a circuit was leaking current to ground and/or the panel ground had a high impedence for some reason then having the panel ground isolated could prevent the input plug body from being hot maybe??
That might be one scenario where it could make a difference, but more likely I’m just inventing things to worry about.
 
OP
OP
Danface

Danface

Well-known member
First Name
Dan
Joined
Sep 19, 2023
Threads
4
Messages
898
Reaction score
912
Location
Central Mass
Vehicles
2023 Lightning XLT
That might be one scenario where it could make a difference, but more likely I’m just inventing things to worry about.
Too much to know, too little time to learn it and too much information and misinformation available = too much to worry about. :)
 
 







Top