v2h8484
Tesla Model 3
A modified 5-15P plug with a wire connected only to the ground pin can be plugged into a 120V outlet of the PPOB to connect the Lightning PPOB to a ground rod for an additional "grounding electrode nearby" as shown in the grounding a bonded generator picture above.
Nice try but that's not code compliant. The code has specific requirements for the GEC including minimum size (e.g. 6 AWG for typical bare copper wire) and connection method (e.g. welded, bolted, etc.) and plug is an allowed method. Also, for SDS, the GEC must be connected at the same point as the ground-neutral bond which is unlikely to be the outlet on the Lightning.
Yes I agree, I believe 6AWG would be required by the code - I had seen a 12AWG generator ground rod system but I hadn't looked it up, which I should have.
6 AWG seems like "overkill" for a 30A max system, but the code only allows smaller wire for "supplemental" grounding equipment conductors.
I stand corrected and updated/edited the previous post.
Yes I agree, 6AWG would be required by the code...I should have looked it up first.
I forgot about this supplemental video that mentions the 6 AWG requirement and how to set it all up with a GENERAC transfer switch...must be getting old...
Upon further reflection...
Perhaps the grounding electrode system of the house to which the Lightning ground system is connected would suffice as the code required "grounding electrode system," as apparently shown by Lorenzo Mari in the figure below, who is an expert in grounding systems - see his bio below. After all it is "connected to the ground terminal on the portable generator" (Lightning PPOB) via the ground wire through the GENERAC and the service panel.
However, since there are apparently conflicting opinions on this, I would err on the side of another grounding electrode system near the truck.
So, I wonder where would be a good place to connect a grounding electrode conductor to the Lightning?
Portable generators often provide an easily accessible ground lug suitable for earth grounding connections. Somewhere easily accessible near the PPOB outlet at the back of the truck would be best.
Has anyone made a grounding connection for a ground rod on their Lightning?
OPTIONAL Background follows
GENERAC transfer switch with a bonded generator - grounding requirements
The GENERAC 6853 transfer switch manual says about grounding requirements for use with a bonded generator as a separately derived system:
Ford F-150 Lightning I need someone to help me respond to this if possible. GENERAC grnd req cod
"...A 'grounding system' and a 'grounding electrode system' shall be 'connected to the ground terminal' on the portable generator. See NEC Article 250.34(A)(4) and (5) for code compliance."
In the NEC, a "grounding electrode system" is the composite of "all installed grounding electrodes" at a building or structure that are bonded together "to provide a low-impedance path to the earth."
The NEC contains a list of items that are permitted to be used as grounding electrodes and requires that if any are present, they must all be used to form the "grounding electrode system."
So all grounding electrodes present at a building or structure should be bonded together to form a single, interconnected "grounding electrode system." And if multiple grounding electrodes are installed at a location, they must all be connected to create one unified system.
There are 8 items that are listed in 250.52 as allowable grounding electrodes: Metal Underground Water Pipe, Concrete-encased Electrode, Metal In-ground Support Structure, Ground Ring, Rod and Pipe Electrodes, Plate Electrodes, Other Listed Electrodes, Other local underground metal systems or structures
Equipment Grounding: This requires connecting non-current-carrying metal parts of the electrical system, like metal boxes, conduits, and appliance frames, to ground.
Grounding System: This comprises all ground wiring, equipment grounding, and generally includes the grounding of the neutral of the electrical system. The purpose is to help stabilize system voltages and aid operation of over-current protection devices during a fault.
A generator equipment frame (e.g., the Lightning chassis) is permitted to be the "grounding system." And on the Lightning, the neutral is bonded to the frame and is part of the grounding system. This "grounding system" is connected to the ground terminal of the Lightning in compliance with code.
Further, when the ProPower OnBoard (PPOB) is powering the house through the GENERAC transfer switch, the "grounding system" via the ground terminal of the PPOB outlet is connected to the GENERAC ground bus, which is in turn connected to the house panel ground bus as in figure 5 below.
The house panel ground bus is connected to a "grounding electrode system," which in my house comprises several outdoor ground rods and an underground cold water pipe.
The NEC requires a "grounding electrode system" for bonded generators when used as a separately derived system, e.g., the Lightning PPOB powering a house. Typically one would see this in the form of a "nearby" ground rod pounded into the earth and connected by a wire to the generator frame.
From what I have read recently, the "nearby" requirement has been loosened/removed and the "grounding electrode system" can be some distance away as long as it provides a low impedance ground path to the earth.
Since the Lightning neutral is bonded to the frame, and the frame is connected to the ground terminal, and the ground terminal is connected to the house "grounding electrode system" and these provide a low impedance path to the earth, then, is a second "grounding electrode system" connected to the Lightning frame required?
Some would say yes, others would apparently say no. The NEC goes through periodic updates and changes, so perhaps that explains why older versions and posts/videos about it, require a nearby grounding electrode connected to the generator frame.
A recent figure by Lorenzo Mari, Figure 5 below, shows what is purported to be a system compliant with the recent NEC code (2023 version) where no additional nearby "grounding electrode system" for the generator is provided (no nearby ground rod to frame). Also note his bio at the end of this post.
Ford F-150 Lightning I need someone to help me respond to this if possible. Fig 5 house system is grounding system
The generator grounding electrode system is apparently the grounding electrode at the service equipment (panel).
The "grounding electrode system" from the generator to the grounding electrode has been highlighted in yellow below (the transfer switch in the highlighted image is shown in the generator connected mode where the grounded conductor - neutral - is switched to the load and not directly connected to the utility neutral).
Ford F-150 Lightning I need someone to help me respond to this if possible. Fig 5 house system is grounding electrode system-path yello
But...
Regardless of Lorenzo Mari's Figure 5 and his expertise, if I want to provide a nearby grounding electrode system for the Lightning, where would be a good place to connect a grounding electrode conductor to the Lightning?
By "good" I mean - easily accessible for connecting to a grounding electrode conductor (#6 wire) and making a good electrical connection to the Lightning chassis (generator frame).
BIO: Lorenzo Mari holds a Master of Science degree in Electric Power Engineering from Rensselaer Polytechnic Institute (RPI). He has been a university professor since 1982, teaching topics as electric circuit analysis, electric machinery, power system analysis, and power system grounding.
As such, he has written many articles to be used by students as learning tools. He also created five courses to be taught to electrical engineers in career development programs, i.e., Electrical Installations in Hazardous Locations, National Electrical Code, Electric Machinery, Power and Electronic Grounding Systems and Electric Power Substations Design. As a professional engineer, Mari has written dozens of technical specifications and other documents regarding electrical equipment and installations for major oil, gas and petrochemical capital projects. He has been EPCC Project Manager for some large oil, gas & petrochemical capital projects where he wrote many managerial documents commonly used in this kind of works.
tearitupsports
Russell
Houston, TX
But...
You keep going back to the Generac system, which is great for those who want that, but it not (on the surface) compatible with the original topic. The Generac transfer switch does not work with Hybrid inverter systems that have an automation transfer switch with generator input. The question at hand is how to make the truck properly and safely work with a Franklin or other brand generator input, where the truck is not the sole source of power, and the entire house loads are still wired to the main, or backup panel. If you can think of a proper wiring scheme to make the Generac work with these sytems, that would be more useful.
In a few years, the bi-directional charger will be the proper and elagant solution.
Sorry, but I did post how to do that in general terms I could have been clearer - review the thread and you will see.
I did something similar with my system because I already had a transfer switch wired for a non-bonded generator, that had to be bypassed when using the Lightning bonded generator through the GENERAC.
The issue of grounding came up as a result on my posting that block diagram and someone saying I hadn't grounded it - I had left off the ground wires for simplification, but then I posted a block diagram WITH the ground wires drawn in.
I think it could be a way to bypass the hybrid inverter system automatic transfer switch, but it would require some rewiring.
In simple terms, you use a GENERAC to switch between the Lightning and the utility, feeding the output to the hybrid inverter transfer switch system which switches between the utility/Lightning (output from the GENERAC output) and the hybrid inverter.
OK, so here I redrew it with the "solar panel hybrid inverter" output and labeled the second transfer switch the "hybrid inverter transfer switch":
Ford F-150 Lightning I need someone to help me respond to this if possible. Block diag of 2 xfer sw hybrid inverter
So the GENERAC manual transfer switch passes through the utility to the hybrid inverter transfer switch when in utility mode, but when the Lightning is connected and powered it can transfer to that source and pass it through to the hybrid inverter transfer switch.
The hybrid inverter transfer switch would switch between the solar panel hybrid inverter output and the utility/Lightning output from the GENERAC.
In the GENERAC, both the hots and neutral would switch between the utility and the Lightning hots and neutral. I gather that the hybrid inverter transfer switch does not switch the neutrals, only the hots, which is like my old transfer switch. I designed this wiring configuration because I did not want to unwire my old transfer switch and remove it from my basement wall (laziness).
That is the concept.
Sorry I didn't make it clearer by redrawing my system's block diagram, but here it is now.
Disclaimer
I am an electrical engineer but not a licensed electrician.
The information provided in this post is provided for information purposes only and does not constitute any endorsement or recommendation. No warranty, expressed or implied, is made regarding the accuracy, adequacy, completeness, legality, reliability, or usefulness of any information found in this post. It is your responsibility to verify and investigate this information.