Well-known member
Nice try but that's not code compliant. The code has specific requirements for the GEC including minimum size (e.g. 6 AWG for typical bare copper wire) and connection method (e.g. welded, bolted, etc.) and plug is an allowed method. Also, for SDS, the GEC must be connected at the same point as the ground-neutral bond which is unlikely to be the outlet on the Lightning.A modified 5-15P plug with a wire connected only to the ground pin can be plugged into a 120V outlet of the PPOB to connect the Lightning PPOB to a ground rod for an additional "grounding electrode nearby" as shown in the grounding a bonded generator picture above.