Last year I installed a Generac 6854 which is the same as the 6852 but includes the Generator Inlet and a 10' four prong cord. All works well however the 10' cord is just too short. I went to Harbor Freight and bought a 25' cord and now I am getting ground fault errors. I exchanged it for another one thinking it might be faulty and the issue continued. I used a multi meter to check continuety and everything checked out. Does anyone here have a suggestion, or possibly a longer cord they have successfully used? I am not interested in snipping the ground so that is not a possibility.

Thanks!
Sponsored

 

chriserx

Well-known member
First Name
Chris
Joined
Oct 3, 2025
Threads
2
Messages
680
Reaction score
501
Location
Louisiana
Vehicles
2025 Ford Lightning Flash Job 2 😭
There has been much discussion regarding transfer switches and I forget the term but effectively multiple ground points. I do not know if it applies to your particular setup but it sure sounds like it.

First thing I'd do is check the ground on the 10' for continuity.
Second thing I'd try is putting the 10' inline with the 25' for a test only.
If it works I'd search for similar grounding issues on the forum regarding the issue and see what the permanent solution was, I know I've seen it but since none of it applies to me I didn't retain it.

Note:
I am not an electrician.
I do not have the 9.6kw PPOB.
I do not have any transfer switch as such.
 
OP
OP
Sullyfamily

Sullyfamily

Member
Joined
May 14, 2024
Threads
2
Messages
12
Reaction score
8
Location
Tx
Vehicles
None
I actually did both of those suggestions. Both the 10' and the 25' continuity test the same. Connecting them together also produces the ground fault. Puzzling!
 

25StarWhiteLightning

Well-known member
Joined
Sep 17, 2025
Threads
1
Messages
57
Reaction score
111
Location
Midwest
Vehicles
2025 Star White Lightning Lariat
This is not electrical advice but what I did was remove the ground from the cable and it won't produce the ground fault anymore. I snipped off the end, cut and capped the ground, and reinstalled a new cord end. It will now only work with bonded generators and/or my Lightning.
 

RLXXI

Well-known member
Joined
Jun 10, 2021
Threads
34
Messages
1,631
Reaction score
1,469
Location
3rd rock
Vehicles
2025 F 150 Flash, 2013 F 150 XLT, 2014 Escape, 2011 Suzuki DR 650SE
Occupation
Automotive Technician
This is not electrical advice but what I did was remove the ground from the cable and it won't produce the ground fault anymore. I snipped off the end, cut and capped the ground, and reinstalled a new cord end. It will now only work with bonded generators and/or my Lightning.
The rv power cord I got came with an adapter that does this.
 

Sponsored

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
4,290
Reaction score
5,734
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
Measure the resistance between each conductor of the 25’ cord with it not connected to anything. If it’s anything less than infinity, the cheap insulation in the cord allows enough leakage to trip the GFCI.
 
OP
OP
Sullyfamily

Sullyfamily

Member
Joined
May 14, 2024
Threads
2
Messages
12
Reaction score
8
Location
Tx
Vehicles
None
This is not electrical advice but what I did was remove the ground from the cable and it won't produce the ground fault anymore. I snipped off the end, cut and capped the ground, and reinstalled a new cord end. It will now only work with bonded generators and/or my Lightning.
Doesn't that defeat the purpose of the neutral transfer switch I bought?
 
OP
OP
Sullyfamily

Sullyfamily

Member
Joined
May 14, 2024
Threads
2
Messages
12
Reaction score
8
Location
Tx
Vehicles
None
Measure the resistance between each conductor of the 25’ cord with it not connected to anything. If it’s anything less than infinity, the cheap insulation in the cord allows enough leakage to trip the GFCI.
Thanks! That's exactly what it was. I will get a better one tomorrow!