Sponsored

Copper vs Aluminum wiring for Charge Station Pro

ericpullen

Well-known member
First Name
Eric
Joined
Jan 4, 2022
Threads
31
Messages
269
Reaction score
485
Location
Louisville, KY
Vehicles
22 F-150 Lightning & 22 Mach-E
Has anyone seen any specifications for the charge station pro that says if it requires copper? I was talking to my electrician and he said that Tesla chargers require copper terminations.
Sponsored

 

F150LER

Well-known member
Joined
Apr 21, 2022
Threads
2
Messages
89
Reaction score
67
Location
Us
Vehicles
F150L
I would imagine it’s copper. Aluminum terminations are pretty specific use cases at this point.
 

PV2EV

Well-known member
Joined
Apr 17, 2022
Threads
55
Messages
695
Reaction score
484
Location
Oregon
Vehicles
2015 Chevy Volt, 2006 Kubota L39, 2006 Suzuki Eige
Would be suprising if it did not take either. If going a distance, use aluminum, and then transition in the junction box.
 

Stlww18

Well-known member
Joined
Apr 12, 2022
Threads
21
Messages
296
Reaction score
417
Location
St. Louis
Vehicles
2022 Lightning Pro, 6/3 blend date
FWIW I asked my electrician about using aluminum to run my 14-50 circuit and he said he thought it was a terrible idea, especially given the price difference isn't significant for most runs you'd expect in a typical home
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
4,039
Reaction score
5,275
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
FWIW I asked my electrician about using aluminum to run my 14-50 circuit and he said he thought it was a terrible idea, especially given the price difference isn't significant for most runs you'd expect in a typical home
For a 50A circuit, that’s true. At 100A, the difference will be significant….about double. Add about $3 per foot of run to use copper.
 

Sponsored

beatle

Well-known member
Joined
Jun 1, 2021
Threads
23
Messages
885
Reaction score
1,003
Location
Springfield, VA
Vehicles
Model S, Ridgeline, Miata, motorcycle(s)
If the charge station specifies copper, perhaps a copper pigtail can be used along with a connector made for Al-Cu junctions with anti-oxidant applied. I know I don't want to pay for 50 feet of copper for the 100A circuit.
 

PV2EV

Well-known member
Joined
Apr 17, 2022
Threads
55
Messages
695
Reaction score
484
Location
Oregon
Vehicles
2015 Chevy Volt, 2006 Kubota L39, 2006 Suzuki Eige

Labs4Lightning

Well-known member
First Name
C
Joined
Mar 30, 2022
Threads
22
Messages
784
Reaction score
692
Location
Maryland
Vehicles
19 150 lariat, 22 lightning lariat blend 4/18/22
If the charge station specifies copper, perhaps a copper pigtail can be used along with a connector made for Al-Cu junctions with anti-oxidant applied. I know I don't want to pay for 50 feet of copper for the 100A circuit.
Not sure why all the anti aluminum talk here.
go look at your service cable coming into your panel. Aluminum.
100 amp circuit with a dab of anti oxidizer ????
when I’m doubt check NEC
 

beatle

Well-known member
Joined
Jun 1, 2021
Threads
23
Messages
885
Reaction score
1,003
Location
Springfield, VA
Vehicles
Model S, Ridgeline, Miata, motorcycle(s)
Not sure if you quoted me accidentally, but I am not anti-aluminum. This isn't the 70s. :) There is definitely a place for it as long as it's done properly, especially as the cost of copper continues its meteoric rise.
 

jefro

Well-known member
Joined
Oct 28, 2021
Threads
3
Messages
699
Reaction score
231
Location
Texas
Vehicles
F150, Corvette, Bolt EV,
I'd think that one could use AL and the manual will have to state it as such or connector will have label. Or label will have it labeled.

There has been a number of ways to get AL to be more reliable. The dielectric grease and use proper torque or they make special ends that can be swedged and used.

Locally your code could be of some issue if you are running a sub panel.
 
Last edited:

Sponsored

F150LER

Well-known member
Joined
Apr 21, 2022
Threads
2
Messages
89
Reaction score
67
Location
Us
Vehicles
F150L
Not sure why all the anti aluminum talk here.
go look at your service cable coming into your panel. Aluminum.
100 amp circuit with a dab of anti oxidizer ????
when I’m doubt check NEC
Not anti, I would be surprised if you didn’t have to switch to copper to make the final connection.
 

tls

Well-known member
Joined
Apr 29, 2022
Threads
22
Messages
476
Reaction score
444
Location
New York
Vehicles
2022 Lightning
If the charge station specifies copper, perhaps a copper pigtail can be used along with a connector made for Al-Cu junctions with anti-oxidant applied. I know I don't want to pay for 50 feet of copper for the 100A circuit.
That connector would be called "the safety disconnect required by code for any charger exceeding 60A". Because the disconnect is a code requirement the transition from Al to Cu is basically free - you use a 2-space, 125A subpanel as the disconnect and put it right by the charger. Run #2 Al into the disconnect - panel main lugs are all rated for Al - and #3 copper for the foot or two (or, heck, just nipple them together if the geometry works) into the charge station. This has been a common way to wire Tesla and Clipper Creek 80A chargers for years.
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
4,039
Reaction score
5,275
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
That connector would be called "the safety disconnect required by code for any charger exceeding 60A". Because the disconnect is a code requirement the transition from Al to Cu is basically free - you use a 2-space, 125A subpanel as the disconnect and put it right by the charger. Run #2 Al into the disconnect - panel main lugs are all rated for Al - and #3 copper for the foot or two (or, heck, just nipple them together if the geometry works) into the charge station. This has been a common way to wire Tesla and Clipper Creek 80A chargers for years.
That works, but is a bit of overkill. A 100 non-fused disconnect switch would cost a fraction of a sub panel with a 125A breaker.
 

tls

Well-known member
Joined
Apr 29, 2022
Threads
22
Messages
476
Reaction score
444
Location
New York
Vehicles
2022 Lightning
I would not use a non-fusible disconnect, and since most of the cheap ones are rated at 50A or 60A for HVAC applications, you may not save as much as you think vs. big-box store prices for a very small panel. The 100A breaker may actually cost more.

That said, check the labelling but most disconnects over 50A should have 90C terminals rated for Cu or Al wire, and be usable instead of my suggested small panel in this application.

Tesla strongly recommends crimping copper ferrules on the supply wiring at the charger end. I would actually use them on both ends of any copper involved (not the Al if used) - unlike Al wire, big Cu still often has rather fine strands and with a 100A OCPD you do not want some little stray copper hair trying to take 100A to ground while there is no actual load connected (!).
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
4,039
Reaction score
5,275
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
I would not use a non-fusible disconnect, and since most of the cheap ones are rated at 50A or 60A for HVAC applications, you may not save as much as you think vs. big-box store prices for a very small panel. The 100A breaker may actually cost more.

That said, check the labelling but most disconnects over 50A should have 90C terminals rated for Cu or Al wire, and be usable instead of my suggested small panel in this application.

Tesla strongly recommends crimping copper ferrules on the supply wiring at the charger end. I would actually use them on both ends of any copper involved (not the Al if used) - unlike Al wire, big Cu still often has rather fine strands and with a 100A OCPD you do not want some little stray copper hair trying to take 100A to ground while there is no actual load connected (!).
Residential HVAC disconnects are generally 50A or less. I’m not referring to those.
more like this:
Ford F-150 Lightning Copper vs Aluminum wiring for Charge Station Pro 251D64F8-1857-42DA-8C3C-F4D120C88B9C


Switching conductor sizes at the transition to take advantage of 90C ampacity is a worthwhile suggestion, but it requires careful attention to detail. The breaker at the supply end will be 70C rated, so it has to be done at both ends.