The OP only mentioned 40. amps. I think you are conflating wiring for a 48 amp charger. Yes, for a 48 amp charger, you need wiring sufficient for 60 amps and a 60 amp breaker.If you are wiring with 6AWG NM-B, aka Romex®, then you are correct. 6/3 NM-B is only rated up to 40 amps.
If you are wiring with THHN in conduit, such as FMC, LFMC , EMT, PCV etc then 9 AWG is good for up to 50 amps.
Another mistake people make when wiring 60 amps is using 6 AWG NM-B Romex®. It is only rated for 55 amps. My electrician used 6-6-8 SEU/CU Copper Service Entrance cable to hardwire my 60 amp Tesla charger. It is similar in looks to Romex® but it is rated for 65 amps where similar Romex® is only rated for 55 amps. The difference is that SEU Conductors are annealed (soft), type THHN/THWN copper conductors.