If you are wiring with 6AWG NM-B, aka Romex®, then you are correct. 6/3 NM-B is only rated up to 40 amps.If you really want 40 amp EV charging, you need 6AWG with a 50 amp breaker.
I would skip the plug - hardwire the charger connection. Less connections to fail and get hot and catch on fire. Also its cheaper anyways. (no box, and no $57 plug).
If you are wiring with THHN in conduit, such as FMC, LFMC , EMT, PCV etc then 8 AWG is good for up to 50 amps.
Another mistake people make when wiring 60 amps is using 6 AWG NM-B Romex®. It is only rated for 55 amps. My electrician used 6-6-8 SEU/CU Copper Service Entrance cable to hardwire my 60 amp Tesla charger. It is similar in looks to Romex® but it is rated for 65 amps where similar Romex® is only rated for 55 amps. The difference is that SEU Conductors are annealed (soft), type THHN/THWN copper conductors.