so what would be needed for an EVSE charger?
That UF-B cable will be fine for a hardwired EVSE with 40A charging or less.

For an EVSE with 48A charging load, #6 THWN in buried conduit is the best option.

For larger EVSE's (e.g., the Ford Charge Station Pro), it depends upon the amount of charging current you want it to offer. At that point, it's pretty much wire-in-conduit and you'll size the wires based on charging loads. For the most common beyond 48A charging (72A charging or 80A charging), you'll want #3 wire in conduit.
Sponsored

 

jefro

Well-known member
Joined
Oct 28, 2021
Threads
3
Messages
699
Reaction score
231
Location
Texas
Vehicles
F150, Corvette, Bolt EV,
If one wanted to set their EVSE at 48A.
May need to run 4 AWG. https://www.galvinpower.org/size-wire-for-a-60-amp-breaker/

An example on This Old House showed their local code install of underground. In the areas that one could get deep enough (and freeze may be part of this too) they could run conduit on a bed of sand. Cover with sand, Then add half dirt. They also then had to run a special yellow ribbon to warn diggers. On the areas they couldn't get to depth their inspector allowed them to concrete over to protect it from digging.
It usually never hurts to run pvc conduit usually your code has to be read. Good thing about direct burial is heat tends to get absorbed.
 
OP
OP

bewbie

Well-known member
Joined
Apr 7, 2022
Threads
31
Messages
409
Reaction score
174
Location
NYC
Vehicles
2022 Lightning Lariat ER Rapid Red
thanks for all the info! i think i will go with the UF-B 6/3 and eventually go with the Juice Box 40. I unfortunately have to run the wire myself and am not efficient in running condiut.
 

rdr854

Well-known member
Joined
Oct 19, 2021
Threads
12
Messages
1,279
Reaction score
888
Location
Northern Virginia
Vehicles
22 Ford F150 Lightning Lariat ER 23 Outback, 25 Volvo EX90 Twin Motor Plus
NEC/NFPA requires the circuit breaker be 25% greater than the evse output amperage. Wire should be sized for circuit breaker rating.
As the home owner you can do what you want and hope nothing happens. A licensed electrician must follow applicable codes.
I thought it was 20%, not 25%. The basis for this is that I needed a 100 amp circuit for an 80 amp charger.
 

Sponsored

tls

Well-known member
Joined
Apr 29, 2022
Threads
20
Messages
447
Reaction score
411
Location
New York
Vehicles
2022 Lightning
UF-B Is direct burial (no conduit), so upgrading to 6-3 would not require larger conduit, or much more cost if distance is not too much. I would do 6-3, 70 amp breaker and 14-50 outlet.
You can't (legally or safely) protect a 50-amp outlet with a 70-amp breaker.
 

PV2EV

Well-known member
Joined
Apr 17, 2022
Threads
53
Messages
691
Reaction score
478
Location
Oregon
Vehicles
2015 Chevy Volt, 2006 Kubota L39, 2006 Suzuki Eige
You may not use a 70A breaker on either a NEMA 14-50 receptacle (50A breaker max) or UF 6-3 conductors. When you use NM cable or UF cable, you must use the 60 degC column for ampacity, and for #6 cable that's only 55A. However, because a 14-50 receptacle is maximum 50A, you may not use more than a 50A breaker to protect it.

The way the NEC works is that it starts with the load. If the load is 55A (after figuring for continuous load requirements or if not required), you select the conductor for the load to be carried (in this case, UF 6/3 would be sufficient), then select the OCPD (breaker) to protect the circuit. Because there is no 55A breaker, a 60A breaker is sufficient.
Right, the 14-50 must have no more than a 50A breaker, and in many places requires a GFCI breaker. This may not work with many EVSE, so hard wiring is a better solution. That is were I was thinking 70A breaker, for a 50A EVSE. Or a 60A breaker for a 48A EVSE.

UF-B is rated for 90c, so should work @ 62.5amps (50amp x 1.25), correct?
 

FlasherZ

Well-known member
Joined
Mar 10, 2022
Threads
9
Messages
915
Reaction score
1,025
Location
St. Louis Metro
Vehicles
F-150 Lightning, Tesla Model X, F250 SD diesel 6.0
Right, the 14-50 must have no more than a 50A breaker, and in many places requires a GFCI breaker. This may not work with many EVSE, so hard wiring is a better solution. That is were I was thinking 70A breaker, for a 50A EVSE. Or a 60A breaker for a 48A EVSE.

UF-B is rated for 90c, so should work @ 62.5amps (50amp x 1.25), correct?
Unfortunately, no. UF cable may be identified at 90 degC, however like NM cable, NEC requires ampacity based on the 60 degC column. (NEC 2017 340.80) #6 UF is only rated to 55A, or a 44A EV charging load.
 

PV2EV

Well-known member
Joined
Apr 17, 2022
Threads
53
Messages
691
Reaction score
478
Location
Oregon
Vehicles
2015 Chevy Volt, 2006 Kubota L39, 2006 Suzuki Eige
Unfortunately, no. UF cable may be identified at 90 degC, however like NM cable, NEC requires ampacity based on the 60 degC column. (NEC 2017 340.80) #6 UF is only rated to 55A, or a 44A EV charging load.
So you get derated twice, once for the continuos load and again for the cable type, wow. So 4-3 UF for a 50A EVSE, or 6-3 THHN in a conduit. Glad my install is in conduit.
 

Sponsored
OP
OP

bewbie

Well-known member
Joined
Apr 7, 2022
Threads
31
Messages
409
Reaction score
174
Location
NYC
Vehicles
2022 Lightning Lariat ER Rapid Red
So a run with 6/3 THHN in conduit will work for a 48A EVSE correct?
 
Last edited:

RickLightning

Well-known member
Joined
Jan 17, 2022
Threads
91
Messages
5,889
Reaction score
7,918
Location
SE MI
Vehicles
'22 Lightning ER Lariat,'22 Mach-E Premium 4X
If the goal is to future proof, then you should run the largest wire that is feasible. I would never consider anything less than a 48amp EVSE, which requires a 60amp breaker, because that future proofs. I did this last summer.
 
OP
OP

bewbie

Well-known member
Joined
Apr 7, 2022
Threads
31
Messages
409
Reaction score
174
Location
NYC
Vehicles
2022 Lightning Lariat ER Rapid Red
If the goal is to future proof, then you should run the largest wire that is feasible. I would never consider anything less than a 48amp EVSE, which requires a 60amp breaker, because that future proofs. I did this last summer.
So #6 in conduit should be ok?
 

RickLightning

Well-known member
Joined
Jan 17, 2022
Threads
91
Messages
5,889
Reaction score
7,918
Location
SE MI
Vehicles
'22 Lightning ER Lariat,'22 Mach-E Premium 4X
So #6 in conduit should be ok?
I am not knowledgeable in code.

If you are running conduit, and could easily swap wire out, then you can make a different decision than if you can't easily swap wire.