My meter is near my drive way, and my panel is already crowded. Can I have an electrician add a new junction after the meter, and install the CSP right there (before my main panel)? It seems as though it would be much simpler than messing with the panel, and then running a new line from the panel all the way back to next to the meter.
Sponsored

 

ericpullen

Well-known member
First Name
Eric
Joined
Jan 4, 2022
Threads
31
Messages
269
Reaction score
483
Location
Louisville, KY
Vehicles
22 F-150 Lightning & 22 Mach-E
You can do that, but it would require a fair amount of work and possibly a service upgrade (depends on how big your current house panel is). You can move from a meter socket to a meter socket that has a built in set of breakers. That's what I did when we did a full panel upgrade last year.

Ford F-150 Lightning Install of Charge Station Pro between Meter and Electrical Panel 1668536988437
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
4,013
Reaction score
5,244
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
In addition to the above, adding the service disconnect at the meter location makes your existing panel a subpanel. The wiring to it will need separate neutral and ground which means 4 wires instead of 3, likely requiring a new run. Then the neutrals and grounds must all be separated in the subpanel.
Discuss details with a reputable electrician.
 

Pioneer74

Well-known member
Joined
Aug 16, 2021
Threads
36
Messages
3,777
Reaction score
6,867
Location
Dearborn
Vehicles
2022 Lightning Lariat ER - 2022 Mach-E Premium
Occupation
Electrician
In addition to the above, adding the service disconnect at the meter location makes your existing panel a subpanel. The wiring to it will need separate neutral and ground which means 4 wires instead of 3, likely requiring a new run. Then the neutrals and grounds must all be separated in the subpanel.
Discuss details with a reputable electrician.
This x2. A lot of work.
 

TaxmanHog

Moderator
Moderator
First Name
Noel
Joined
Jan 19, 2022
Threads
206
Messages
14,997
Reaction score
16,543
Location
SE. Mass.
Vehicles
2022 Lightning Lariat-ER & 2024 HD Road Glide CVO-ST
Occupation
Retired
Post 2 resembles what my plan B would have been if I was not successful getting the second service to my garage.

Agree with following posts, the meter pan with two 200 amp double pole breakers, one feeding house the other feeding your garage, then conduit with ground, neutral, A & B hots to another load center from which the 100 amp breaker feeding to the FCSP.
 

Sponsored

Akbrian

Well-known member
First Name
Brian
Joined
Sep 21, 2022
Threads
3
Messages
100
Reaction score
91
Location
Alaska
Vehicles
F150 Lightning 2022
At the meter there is likely a breaker there hopefully 200Amp. Like previous post said, two options depending on main panel add another breaker and feed the charger or splice in and add a subpanel. My service box wouldnt accept another breaker so spliced in after main breaker with proper mechanical connectors and fed a subpanel. My house panel was a 45 foot run with sheet rock and or conduit so was easier and cheaper to go 70 feet underground back to the meter, put the subpanel in and power off that also added RV power and backup 50amp receptacle at charger location so if charger stops can still charge with receptacle power.
 
OP
OP

xycarp

Well-known member
Joined
Jul 21, 2022
Threads
22
Messages
58
Reaction score
48
Location
SE Michigan
Vehicles
2021 Bronco Sasquatch, Lighting Lariat ER on order
More details…. I have two meters. One feeds the main panel. The other feeds a very simple fuse box on the outside of the house, next to the AC that it serves.

What if I replace that fuse box with a mini panel that supplies both the AC and a charger?
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
4,013
Reaction score
5,244
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
More details…. I have two meters. One feeds the main panel. The other feeds a very simple fuse box on the outside of the house, next to the AC that it serves.

What if I replace that fuse box with a mini panel that supplies both the AC and a charger?
Sounds like a good plan as long as it’s OK with your utility. Why do you have a second meter? If it’s for a special HVAC rate, the utility may not allow other loads.
 

Pioneer74

Well-known member
Joined
Aug 16, 2021
Threads
36
Messages
3,777
Reaction score
6,867
Location
Dearborn
Vehicles
2022 Lightning Lariat ER - 2022 Mach-E Premium
Occupation
Electrician
More details…. I have two meters. One feeds the main panel. The other feeds a very simple fuse box on the outside of the house, next to the AC that it serves.

What if I replace that fuse box with a mini panel that supplies both the AC and a charger?
I remember having something like that as a kid. It was called "interruptable service". It was a way to get a special rate for the air conditioning because the utility provider could shut it off during peak demand.

Before doing anything with that circuit you should check with your utility to make sure that it can be altered and that it has the capacity to support the load of the EVSE.