Question for those out there with fleets or similar needing slightly "faster charging".
Back story - we have been charging with Level 2's and recently installed 25 kw DC chargers. Fallen in love with the 22-23 kw "net" speed and the increased up time this gives our trucks - however the DC charger shuts down when "done" and does not reactivate for pre-conditioning/departure times. This is a BIG issue for us as its still below freezing here and the trucks are used around the clock - having a preconditioned battery is essential.
We do have a Ford 80 amp, it works "okay" but I would like to get the extra 5+ kws of the Lightnings possible 23 kw (dual 11.5 kws) and we have the power/space to go to a 150 amp breaker (120 useable). I have not found a charger above the 19.2/80 amp FCSP (or other) in North America - I see UK ones that are three phase. Does anyone know of a UL/ULC rated one available?
Thanks
Back story - we have been charging with Level 2's and recently installed 25 kw DC chargers. Fallen in love with the 22-23 kw "net" speed and the increased up time this gives our trucks - however the DC charger shuts down when "done" and does not reactivate for pre-conditioning/departure times. This is a BIG issue for us as its still below freezing here and the trucks are used around the clock - having a preconditioned battery is essential.
We do have a Ford 80 amp, it works "okay" but I would like to get the extra 5+ kws of the Lightnings possible 23 kw (dual 11.5 kws) and we have the power/space to go to a 150 amp breaker (120 useable). I have not found a charger above the 19.2/80 amp FCSP (or other) in North America - I see UK ones that are three phase. Does anyone know of a UL/ULC rated one available?
Thanks
Sponsored