240 volt charging wall receptacle gets very warm 14-50R bryant

DiveMan911

Well-known member
First Name
R.J.
Joined
Feb 24, 2022
Threads
6
Messages
167
Reaction score
186
Location
Maui, HI
Vehicles
'06 Acura TL, '13 Ford Escape
Occupation
Flight Nurse
Update on my overheating receptacle issue.
I opened up the outlet and I can’t tell exactly which size the THHN is, however it is solid copper and it’s either 12 or 10ga, so big enough for 30amps (edit…20amps). I tightened down the lugs. They were reasonably tight, but I really cranked them down. It was still warm. I basically determined this is likely an issue with the EVSE so I started troubleshooting it.
I opened up the EVSA itself with a plan to replace the wall side plug. It’s an early generation Lectron charger. What I found is disappointing. Although it’s a four wire (three conductor) plug (NEMA 14-30)…only 2 conductors are being utilized. Which I would imagine is what’s causing the heat. I’ll be finding a different EVSE.
Sponsored

 
Last edited:

TaxmanHog

Moderator
Moderator
First Name
Noel
Joined
Jan 19, 2022
Threads
194
Messages
14,432
Reaction score
15,713
Location
SE. Mass.
Vehicles
2022 Lightning Lariat-ER & 2024 HD Road Glide CVO-ST
Occupation
Retired
Update on my overheating receptacle issue.
I opened up the outlet and I can’t tell exactly which size the THHN is, however it is solid copper and it’s either 12 or 10ga, so big enough for 30amps. I tightened down the lugs. They were reasonably tight, but I really cranked them down. It was still warm. I basically determined this is likely an issue with the EVSE so I started troubleshooting it.
I opened up the EVSA itself with a plan to replace the wall side plug. It’s an early generation Lectron charger. What I found is disappointing. Although it’s a four wire (three conductor) plug (NEMA 14-30)…only 2 conductors are being utilized. Which I would imagine is what’s causing the heat. I’ll be finding a different EVSE.
The ground was not used?
Only the two HOTs were connected?
 

Whammy Bar

Well-known member
Joined
May 30, 2022
Threads
29
Messages
772
Reaction score
1,277
Location
SoCal
Vehicles
2022⚡Lariat ER 🍋ed Reliable-1971 F100 2019 Tesla 3 LR
Occupation
Electrician
Update on my overheating receptacle issue.
I opened up the outlet and I can’t tell exactly which size the THHN is, however it is solid copper and it’s either 12 or 10ga, so big enough for 30amps. I tightened down the lugs. They were reasonably tight, but I really cranked them down. It was still warm. I basically determined this is likely an issue with the EVSE so I started troubleshooting it.
I opened up the EVSA itself with a plan to replace the wall side plug. It’s an early generation Lectron charger. What I found is disappointing. Although it’s a four wire (three conductor) plug (NEMA 14-30)…only 2 conductors are being utilized. Which I would imagine is what’s causing the heat. I’ll be finding a different EVSE.
Conductors need to be sized for continuous load. So if you're rocking yellow romex (12ga) your limits 16A. If you have the Halloween orange (10ga) then your limited to 24A.
 

TaxmanHog

Moderator
Moderator
First Name
Noel
Joined
Jan 19, 2022
Threads
194
Messages
14,432
Reaction score
15,713
Location
SE. Mass.
Vehicles
2022 Lightning Lariat-ER & 2024 HD Road Glide CVO-ST
Occupation
Retired

Sponsored

TaxmanHog

Moderator
Moderator
First Name
Noel
Joined
Jan 19, 2022
Threads
194
Messages
14,432
Reaction score
15,713
Location
SE. Mass.
Vehicles
2022 Lightning Lariat-ER & 2024 HD Road Glide CVO-ST
Occupation
Retired
Sorry, I'm confused................. two discussion on this thread.
 

DiveMan911

Well-known member
First Name
R.J.
Joined
Feb 24, 2022
Threads
6
Messages
167
Reaction score
186
Location
Maui, HI
Vehicles
'06 Acura TL, '13 Ford Escape
Occupation
Flight Nurse
Conductors need to be sized for continuous load. So if you're rocking yellow romex (12ga) your limits 16A. If you have the Halloween orange (10ga) then your limited to 24A.
It’s not Romex, it’s THHN in conduit. Conductors are wrapped in electrical tape identifying them, so I can’t read their size. I also don’t have a guage tool, so I was eyeballing it. Basically, an exact science. It’s definitely big enough for a 20 amp breaker, just seems silly they did a 20amp breaker on a 30amp receptacle.
 

chl

Well-known member
First Name
CHRIS
Joined
Dec 16, 2022
Threads
6
Messages
1,302
Reaction score
743
Location
alexandria virginia
Vehicles
2001 FORD RANGER, 2023 F-150 LIGHTNING
Dielectric grease is an insulator, not a conductor. There is no manufacture that recommends usage of any grease or lubricant on lugs. In fact the torque specs for typical commercial 14-50 outlets made by Hubbell and Bryant are Dry Torque Specs.

The only wire connections that should have a chemical at the lugs are when using aluminum wires on lugs certified for aluminum. Then usage of something like NOALOX anti-Oxidant compound is REQUIRED. This is usually found on service entrance aluminum feeder cables.
Yes, dielectric grease if applied to protect against corrosion should be applied only after the terminal/wire contact is torqued properly. So for example, it is applied to the exposed parts of car battery connections AFTER they have been mounted and tightened.

See for example:

If the outlet is located in an area that is subject to moisture formation, then using a weather-resistant outlet box type is a must to prevent corrosion, and your local code may require it in garages.
 

chl

Well-known member
First Name
CHRIS
Joined
Dec 16, 2022
Threads
6
Messages
1,302
Reaction score
743
Location
alexandria virginia
Vehicles
2001 FORD RANGER, 2023 F-150 LIGHTNING
thanks Brons2. my EVSE (in the pic) was also a Amazon cheapie bought in 2020 for our PHEV Pacifica. The cheapie HD 14-50R outlet lasted 3 years before melting.

With the Lightning needing longer charging and up to the max 32A the EVSE is able to provide, I changed the cheapie outlet for the Bryant, but I guess I need to replace the romex as well and maybe the breaker - here in Florida its hot and humid, the circuit breaker panel inside the garage is showing signs of corrosion on the bus bars (where the breaker connection is seated. Perhaps I need to turn off the main and lightly sand the bus bars prior to installing a new breaker and wiring - but I must be getting old it was tough running the wire into the receptacle box and connecting the Bryant 14-50R and then getting the receptacle into the box once connected.
Sanding could/would create pitting which is a bad thing for electrical connections.

There is contact cleaner you can use if needed.

However, you should use a weather tight panel in your area of high humidity.

BTW, overheating can be mistaken for corrosion, both can caused a 'brown' discoloration of plastic parts in outlets in my experience. Of course corrosion can cause hot spots and overheating.