Just got my Ford Promise charger installed (Emporia Classic hardwired for 48A). During install they told me they planned to install 6/2 romex and I told them they can't for full rating on 60A breaker so they agreed to switch to MC cable.

I am doing a charge from 70% to 100% (road trip tomorrow) and checked on it about every 15 minutes. I noticed the cable and breaker were getting warm. At about 1 hour in I took some temperature readings. The breaker was about 122F at the surface of the breaker and the cable was about 123F where it was sitting wrapped around the charger.

Two questions:
  1. Is the 60a breaker getting too hot?
  2. Is the cable getting too hot?
I read the Emporia manual it doesn't specifically say the cable needs to be unwound during charging, but it might make sense (although a huge nuisance) to unwind it.

Garage ambient was probably 73F.

What is everyone else seeing?

Ford F-150 Lightning First Time EV Owner - New Emporia Classic at 48A. Is this too hot? IMG_2720
Ford F-150 Lightning First Time EV Owner - New Emporia Classic at 48A. Is this too hot? IMG_2717
Sponsored

 
Last edited by a moderator:

bmwhitetx

Well-known member
First Name
Bruce
Joined
May 21, 2021
Threads
45
Messages
2,690
Reaction score
3,800
Location
DFW-Texas
Vehicles
2022 F150 Lightning Lariat ER
Occupation
Retired engineer
I've never measured it but I would expect it to get a little warm. Will depend on ambient of course.

I have that charger on a 60A breaker as well and I typically use the Emporia app and change amps to 40A. It's overnight and I'm not in a rush so no need to run at the limit. I will if I need to. Heat produced is I squared R, so reducing the current reduces heat by the square.
 
OP
OP
25StarWhiteLightning
Joined
Sep 17, 2025
Threads
1
Messages
4
Reaction score
2
Location
Midwest
Vehicles
2025 Star White Lightning Lariat
Good idea on setting the power down. I was really wanting to stress test it as it was just installed. I will likely be good with derating to 40A as well.

Would love it if someone else could measure their temperatures after about an hour of full bore charging.
 

mattbrac3

New member
First Name
Matthew
Joined
Oct 2, 2025
Threads
0
Messages
4
Reaction score
2
Location
Ramona, CA
Vehicles
25’ Lightning Lariat in Antimatter Blue Metallic
Occupation
Local Pig
I cannot speak to the 60A specifically, but I know when I am charging at 38A from my wall charger, the cable and breaker do get warm, but so do my other breakers for the A/C and such when they are running at full tilt in the summer. Not sure if that helps or not.
 

JMD359

Active member
First Name
One843657295470895!
Joined
Dec 27, 2024
Threads
0
Messages
30
Reaction score
15
Vehicles
22 F150 Lightning Lariat,2022 Toyota Rav4 Prime,2011 F350 6.2L
Occupation
Mechanic
This why it’s always best to tie it down from the max rated output your paying to heat your breaker and wiring … that would be safer and more efficient at 32 or 40 amps . Everything will last longer too. Less is more . A so think it’s all normal your running the max allowable amperage thru it for longer periods of time
 

Sponsored

kf59

Active member
First Name
Ken
Joined
Oct 25, 2024
Threads
1
Messages
32
Reaction score
31
Location
4$a7Yaofbfutc
Vehicles
F150 Lightning
I've never measured it but I would expect it to get a little warm. Will depend on ambient of course.

I have that charger on a 60A breaker as well and I typically use the Emporia app and change amps to 40A. It's overnight and I'm not in a rush so no need to run at the limit. I will if I need to. Heat produced is I squared R, so reducing the current reduces heat by the square.
You’re still well below melting point for most plastics, but generally speaking a breaker under full load should only be slightly warmer than ambient temperature. At a minimum, I would check to make sure that the wires are adequately seated into the breaker and that your electrician used the proper gauge wire. In my experience, faulty breakers off the shelf are much more common than one would expect. If smell anything, it’s time to shut it down.
 

Newton

Well-known member
Joined
May 27, 2021
Threads
11
Messages
478
Reaction score
633
Location
WA State
Vehicles
VW e-Golf, 2023 Lightning Lariat SR, Kia EV6, Toyota T-100
This is a consequence of higher amperage continuous charging. This is the electrical equivalent of leaving an electric oven on “broil” for hours with the oven door open. Wires are going to get hot.

You definitely want to unwrap the cable if you are going to charge at that amperage. Personally I see little value in charging at higher amperage, if I had a higher amperage charger my truck would be recharged at midnight rather than 2AM. Your mileage may vary.

Your terminations are probably rated for 60C (140F)
 

Lytning

Well-known member
Joined
Jan 8, 2022
Threads
9
Messages
591
Reaction score
965
Location
Georgia
Vehicles
Prev: 2000 SVT Lightning; Now: 2022 BEV Lightning
Occupation
Engineer
This why it’s always best to tie it down from the max rated output your paying to heat your breaker and wiring … that would be safer and more efficient at 32 or 40 amps . Everything will last longer too. Less is more . A so think it’s all normal your running the max allowable amperage thru it for longer periods of time
I agree. I have a 50 amp breaker and initially set the charger at 40 amps. The breaker would operate at about 125 F. I stepped down to 32 amps and the breaker now operates under 100 F. I believe in charging slowly if faster charging is not required to keep up with driving needs.
 

bryce

Well-known member
First Name
Bryce
Joined
Jan 30, 2025
Threads
5
Messages
61
Reaction score
65
Vehicles
2023 Lightning Lariat ER, 1999 Boxster
Charging my '23 Lariat on my FCSP, 80 amp breaker but have it set at 60 amp/12 kWh charge rate. The breaker temp measures 78 degrees, slightly above ambient at 65 degrees but not hot. The FCSP measures 83 degrees.
 

Sponsored

B177y

Well-known member
First Name
Bill
Joined
Jul 16, 2024
Threads
12
Messages
499
Reaction score
610
Location
Oly Pen, WA
Vehicles
2024 Pro ER Max Tow
Just got my Ford Promise charger installed (Emporia Classic hardwired for 48A). During install they told me they planned to install 6/2 romex and I told them they can't for full rating on 60A breaker so they agreed to switch to MC cable.
^^ This is the most concerning part of your post to me. The electrical contractor had to be "convinced" to use the proper wiring? This contractor was part of the Ford Power Promise deal?

As for your temperature, that's completely normal. I have a 60 amp breaker feeding a 48 amp hardwired Emporia through a short run of up-sized 3 awg in EMT conduit. The breaker gets warm, never measured but your observation seems reasonable. The Emporia cable always gets warm, again your observation seems reasonable. I have read that it is best to uncoil the cable while charging. My charger is next to my charge port so I keep my cable in a single large loop so that ther is only one layer of cable while charging to more easily dissipate the heat.
 
OP
OP
25StarWhiteLightning
Joined
Sep 17, 2025
Threads
1
Messages
4
Reaction score
2
Location
Midwest
Vehicles
2025 Star White Lightning Lariat
^^ This is the most concerning part of your post to me. The electrical contractor had to be "convinced" to use the proper wiring? This contractor was part of the Ford Power promise deal?
Yes through QMERIT. I took the day off work to make sure they did everything right. My first question to them was what wire they were using. He had me talk on the phone with their master electrician who tried to convince me Romex is fine and they do it all the time.
They agreed to do MC cable and didn’t charge me extra but concerning. I wonder if I can tell QMERIT somehow.
It was inspected but he didn’t ask much and was there for all of 5 minutes.
Thanks for feedback on temp. I knocked the charger down to 40a and still see temperatures at that level next.
 

RLXXI

Well-known member
Joined
Jun 10, 2021
Threads
23
Messages
897
Reaction score
709
Location
S. E. Louisiana
Vehicles
2025 F 150 Flash, 2013 F 150 XLT, 2014 Escape, 2011 Suzuki DR 650SE
Occupation
Auto tech
I have mine set to the max of 48A and leave most of the cable coiled up. Never an issue. 122°f isn't very hot at all. Your water heater is typically preset to 120°f.

Normal human temp is almost 100° (98.6°) so if you think of it in relative terms, yeah, your temp reading is fine.