tearitupsports
Russell
Cypress, TX
Thanks for that reply. I actually work for an electrical contractor, and we specialize in backup power systems - Several ESS battery manufacturers as well as Generac install and service. I have had several customers approach me about how to use the Lightning to extend their batteries in certain situations. This is a very helpful thread.
I definitely think you are on the right track. I think the best system for people right now is a smaller home battery (15-20 kWh), a small solar system (5+ kW), a bi-directional charger for the EV, and a small generator to have for emergency. Right now almost everyone is pushed to have a large version of one of these, but the new systems make it super easy to have a much lower cost mix.
Currently the Franklin, Sigenergy (Pointguard), and Sol Ark are all capable of this I believe. EG4 and Ecoflow have systems that are pretty close, but don't have quite all the features yet.
doggod
Jef
Mendocino County, California
cybertruck, f150 lightning, 911 turbo s
I plug the 240 volt plug from Lightning and Cybertruck into my EG4 inverter to charge house batteries when we have bad weather in winter and get no sun. works awesome. had to get an adapter for cybertruck as I got lightning first so I bought extension cord for it.
MapleMan650
Santa Cruz Mountains
'22 Ford Lightning Lariat ER, 2017 Ford Mustang GT
I.T.
Hey everyone, I've attached the White Paper from FranklinWH to my original post. Here are some highlights from the document.
They acknowledge the grounding issue and state that ground wire does need to be disconnected.
For the Ford F150, the NEMA 14 plug connecting to the F150 will need to have its ground wire disconnected. If it remains connected, the truck’s electrical system will show a ground fault error.​
Please note that the above-mentioned set-up does not require any additional hardware from the EV manufacturer and should only be used during an extended outage when other system generation sources (PV, Stationary/Mobile Generator) are not available or adequate to serve consumer demand. Also note that grounding at the truck needs to be removed to prevent any ground fault errors.
The EV with V2L functionality behaves as a portable generator on wheels with the primary goal of feeding the home loads and using any excess capacity to charge the aPowers. For faster aPower charging, keep home loads under 1 kW.
Does FranklinWH support V2H as well? No, it’s important to note that the FranklinWH system supports V2L only and does not currently support V2H bi-directional charging. However, it is on the product roadmap of FranklinWH to support V2H. The aGate’s robust 280 A busbar and Energy Management System has the capability to manage many power sources including bidirectional charger.
MapleMan650
I.T.
Also, I just received this from their engineering team when I asked them about the configuration.
Regarding your question about grounding: your approach of removing the ground connection between the truck and your generator inlet is consistent with the guidance in our Vehicle-to-Load (V2L) white paper, and it’s the right step to avoid GFCI tripping.
From an electrical theory standpoint, a system does not always require a separate grounding connection. For example, older 3-wire dryer hookups used the neutral as both the grounded conductor and the equipment bond without requiring a separate equipment ground. Similarly, when a generator is not considered a separately derived system (as defined in NEC Article 100), and the neutral is not switched between the generator and the main service, it does not require its own grounding electrode. In those cases, bonding and grounding are maintained through the service equipment in accordance with NEC 250.30 and 250.24(A)(5).
In your FranklinWH + Lightning setup, the truck is not operating as a separately derived system. By removing the extra ground connection, you’re preventing parallel grounding paths that can confuse protective devices such as GFCIs. The FranklinWH V2L white paper addresses this directly: when the vehicle connects, the grounding and bonding reference remains at your home’s service equipment, not in the truck. This keeps the system in alignment with NEC 702.11 and 250.6, ensuring safe operation without objectionable current paths.
So, to address your concern, removing the ground wire in this context is not unsafe. In fact, it prevents ground loop issues, avoids nuisance GFCI tripping, and ensures the system behaves as intended. The FranklinWH system is designed with CTs, relays, and intelligent controls to manage power flow safely, and the proper grounding path remains established through your service equipment.
We truly appreciate your attention to detail and your focus on safety. If you have any further questions, don’t hesitate to reach out, we’re happy to clarify.
v2h8484
Tesla Model 3
What they told you is misleading and wrong. There is no exception in code for generators that connect to house wiring to be ungrounded. It doesn't matter if the generator is a SDS or not. It also doesn't matter if the generator has GFCI or not. Given the number of code sections they referenced it seems they have some code knowledge. So, it's rather suspicious that they conveniently left out NEC 250.20 and 250.21 that clearly state grounding requirements and exceptions.
I am glad you like your system but I would not trust the company for code compliance.
I am glad you like your system but I would trust the company for code compliance.
I agree with you - not having an EGC to the truck is technically a code violation.
But the way it’s implemented, it’s not unsafe.
v2h8484
Tesla Model 3
I agree and my position has always been that code compliance does not necessarily mean safe and vice versa. However, I do want to call out misleading/wrong info especially from companies that can make people think something is code compliant when it's not.
MapleMan650
I.T.
🍿🍿 Thank you @v2h8484 and @Maquis. I am not an electrician or electrical engineer and only know enough to be dangerous. I am happy to hear that you both believe the setup is safe even though it may be against code. This setup will be rarely used so I'm comfortable with a safe, non-code compliant solution. @v2h8484, I sent your reply to the engineering team to see what they say. I also gave them a link to this thread to see if they can jump on directly.
Jay@FranklinWH
Jay
F-150 Lightning
Product Manager
Thank you @MapleMan650 @v2h8484 @Maquis for highlighting the need to clarify the code compliance of this use case, and I'll confirm that our documentation is updated. I'm glad to see that users are happy with the feature and are able to use their Ford Lightning in ways that they may not have originally anticipated.
This is an interesting topic, and it's important to both get it right and understand that while very specific code sections must be referenced, it is in fact code-compliant. While there seems to be some confusion, hopefully this will help share some insight on what is clear guidance under the NEC (2020 & 2023 NFPA 70 referenced below), which everyone can access. Please use the references below to confirm:
As EVs equipped with a receptacle(s) for the purposes of exporting power to supply utilization equipment ("EVPE") must follow similar safety requirements as required by the NEC for other sources, such as portable generators (NEC 625.60 - AC Receptacle Outlets Used for EVPE), these guidelines apply:
  • Conductor to be grounded, AC systems: NEC 250.26, ...if generator is "separately derived," (NEC 250.34(C))
  • Separately Derived System (2023 NEC 100 Definitions) "...supply output having no direct connections, ...other than those established by grounding and bonding connections."
  • Grounding and Bonding: NEC 250.34(B), for a vehicle mounted generator using a receptacle and a cord-and-plug connection to system equipment ("shall not be required to be connected to a grounding electrode")
Because EVPE are not to be connected to the "Area EPS" (grid), they are integrated at a specifically controlled system input source on the certified & listed FranklinWH ecosystem (the V2L/generator input), and only usable during an islanding event, or if the system is used off-grid only.
Regarding the specifics of the EVPE outlet used under NEC 625.60(D), "various methods" can be used to provide for GFCI requirements (e.g. the Ford Lightning's certified/integrated circuit protection, trip indicator, and reset control button).
**Putting all of the above together, the GFCI outlet of certified EVPE, like the Ford Lightning, can safely supply "off-board utilization equipment" (the V2L system inlet receptacle) without itself needing to be connected to a grounding electrode as defined in 250.52 ("Grounding Electrodes"). This is because they are by definition not a "separately derived system," and proper guidance for their use is otherwise comprehensive. This means that while the home itself and all other system components remain grounded/bonded as needed (NEC 250.20), the V2L system inlet receptacle equipment, which is only in use (energized/connected) when the EVPE is in use, it "shall not be required to be connected to a grounding electrode," in compliance with NEC 250.34 (vehicle mounted, etc.) and NEC 250.20 (AC Systems to Be Grounded "unless prohibited elsewhere in this Code").
[*EDIT: Whenever there is a question related to code compliance, this word always comes up: "interpretation." This can mean a couple things.
The reality is that only the AHJ can make a "decision" on code-compliance whenever there is a question, and that, too, is linked to "interpretation" (even when there may be different interpretation decisions within one AHJ - e.g. plan reviewer #1, #2, inspector #1, #2, etc).
Among those really concerned and most knowledgable, the answer usually leans towards, "well, in the next code cycle, maybe this will be fixed."
All any responsible OEM can do is make a tested, safe product, and offer a path to code compliance based on as much of the currently published & approved text - which ultimately is also an interpretation up to the AHJ.]
NW Ontario Ford Lightning
Robert
NW Ontario Canada
Contractor
For anyone interested and following along home solar with V2L back-up:
The other option is DC charging the home battery from the EV; ie using an EG4-chargeverter powered by EV AC-output the chargverter can be set up to add energy into the home battery DC.
There is no ground connection to interfer with the home AC system because the EV AC is never connected to the home AC in this set up.
There will be some extra loses due to double conversion EV-DC to EV-AC then Chargeverter-DC output.
It is simple, and can run off of any EV with an AC output, 120 or 240 are both usable with a Chargverter. It can also run off a very small "suitcase" generator if needed.
It is safe, and complies with all code requirements without any modifications, or special understanding of electicity.
It is easy for non-electrically-trained persons to use it - ie my spouse and family can plug it in and it works, and I know they can do it even if I am away.
You can program the chargeverter to charge at any rate of charge you like, and to taper off the charging as your home battery ESS reaches full SOC.
It allows the home battery to take any high current in-rush (say air con, or well pump start up) with no affect what so ever on the EV.
Low and steady charging - if your home uses 24kWh per 24 hours "say" - then you can just set the EV-Chargeverter charge rate to 1kWh per hour (1kW) and allow the home battery to take out the peaks and low's of power use from the house loads. All you need to supply from the EV is the daily average energy, not the largest peak load.
For the older Lightnings' that need a steady 300W draw in order to Not shut down pro-power, this set up works perfectly as well.
A final bonus - if you charge at a set rate, you know in advance how long the EV can power the home - ie 1kW charge rate will use 24kWh per full day. If you know you can spare 50kWh from the truck, you know you have at least 2 full days you can be powering the home. - no guess work required.
- Solar powered home and business for four years.
Solar panels 13 kW
Inverters 36kW max continuous output (150A 240vAC)
LiFePO4 battery bank - 142 kWh storage capacity.
tearitupsports
Russell
Cypress, TX
Solar panels 13 kW
It’s important to note that the chargeverter will only work with 48v battery systems like sol ark and eg4. That is not an option for Franklin or Sigenergy.
for the systems it works with though it is a nice option with the benefit of good isolation.
Robert
NW Ontario Canada
Contractor
Most home solar battery systems are "48volt nominal" lithium-iron-phosphate, which operate between 48v DC and 56v DC. The two largest firms that supply home energy storage (Tesla and Sunrun) both use 48volt nominal. The EG4 chargeverters are an easy method for the non-electrically trained. Other DC chargers can be used to accommodate other battery voltages.
HVDC batteries are not very common in home solar - at least, not yet.
For now, "48volt" is by far the most common.
v2h8484
Tesla Model 3
There are several incorrect and confusing statements in the above and I have no interest in addressing them all. As an example, I will just point out that you are misstating what NEC 250.34(B) allows. It only allows a vehicle mounted generator to be ungrounded if it only supplies loads on the vehicle and/or cord and plug loads connected directly to outlets on the vehicle.
You may not like or agree with the code but any generator connected to house wiring must be grounded in order to be code compliant. EV V2X maybe new but vehicle mounted generators are certainly not. They have been around for decades and the code is clear about their grounding requirements. BTW, the code is subject to vendor influence so I would suggest companies like yours try to get representation on the code making panel to change it to be more friendly for your products. As an example, my understanding is that NEC 250.34(B) came about due to heavy influence on the CMP by the entertainment industry.
