Jay@FranklinWH
New member
@v2h8484 - I actually expected some followup might be needed. Is that your interpretation of this? Please confirm.There are several incorrect and confusing statements in the above and I have no interest in addressing them all. As an example, I will just point out that you are misstating what NEC 250.34(B) allows. It only allows a vehicle mounted generator to be ungrounded if it only supplies loads on the vehicle and/or cord and plug loads connected directly to outlets on the vehicle.
You may not like or agree with the code but any generator connected to house wiring must be grounded in order to be code compliant. EV V2X maybe new but vehicle mounted generators are certainly not. They have been around for decades and the code is clear about their grounding requirements. BTW, the code is subject to vendor influence so I would suggest companies like yours try to get representation on the code making panel to change it to be more friendly for your products. As an example, my understanding is that NEC 250.34(B) came about due to heavy influence on the CMP by the entertainment industry.
(it appears to not be "loads," as you suggest, but connected "equipment through receptacles mounted on the generator," and the definition of "equipment" and 250.20 main title acknowledges allowance for this.)[*copyrighted content shared for educational purposes]