Have you tested it?
I have a similar setup but when we had a power outage, the truck would not allow the connection and would throw the breaker on the 30amp connection in the truck.
But when I hooked it up to generator the Generlink worked fine. Not sure why yet
Yes it works great. But I also got the disconnect problem when I first plugged in the Lightning.

To resolve it I had to disconnect the ground line between the generator plug (where the Lightning plugs in) and the Generac panel. The Lightning apparently doesn't like the bonded neutral (lots of discussion about this on the forum). The outlets are still grounded inside the panels, but the truck ground (how can it have a ground if it's on rubber??) is not connected.

Similarly, the Emporia charger showed an error (2 slow, 5 fast LED flashes), with continuous beeping when I plugged it into the off-grid inverter. Turns out it REQUIRES a bonded neutral. To resolve this I simply connected the neutral and ground from 14-50R plug together in the neutral connection on the inverter. Problem solved.
Sponsored

 

flyct

Well-known member
First Name
Jerry
Joined
Sep 28, 2023
Threads
38
Messages
975
Reaction score
1,135
Location
South Florida
Vehicles
2024 Ford Lightning Platinum & 2ea-2026 Tesla Juniper Model Ys
Occupation
Blissfully Retired
Have you tested it?
I have a similar setup but when we had a power outage, the truck would not allow the connection and would throw the breaker on the 30amp connection in the truck.
But when I hooked it up to generator the Generlink worked fine. Not sure why yet
The reason it throws the breaker on the truck is the truck senses a ground fault because the Neutral and Ground are bonded together at your house by code.

If you disconnect the ground connection from your truck to the house generator inlet it would work and the truck’s breaker would not instantly trip. All your outlets and appliances in your house would still be grounded through your house wiring. All the GFCI outlets will still trip if they had a Ground Fault.

I’m not recommending you do this but talk to your electrician for advice.
 
Last edited:

Maxx

Well-known member
Joined
Jul 15, 2021
Threads
48
Messages
2,243
Reaction score
2,678
Location
MD
Vehicles
23 Pro, Sky RL, Frontier, Aurora V8, Buicks, ....
Being ready for outage is like taking an umbrella with you on a cloudy day. Umbrella ensures it will not rain.

I had multi day outage in middle of a winter right before I got the lightning. Then I rewired a few things so that I could easily heat the house and power the router/fridge/…. With a 220 extension cord/splitter. It has been 3 years and I have yet to have an outage long enough to justify plugging in.
 

hajalie24

Well-known member
Joined
Aug 10, 2024
Threads
10
Messages
95
Reaction score
90
Location
USA
Vehicles
2024 F-150 Lightning Lariat Antimatter Blue
That's interesting - how? That sounds like a good way damage something. The Lightning certainly is not expecting to be paralleled with another power source, and the PowerWall expects a grid connection that can source or load an very large amount of power (which the Lightning can not).
DC power supply connected to a "grid tied inverter"
 

Henry Ford

Well-known member
First Name
John
Joined
Dec 21, 2022
Threads
9
Messages
1,648
Reaction score
2,378
Location
Michigan
Vehicles
2022 F150 Lightning Platinum
most of us will admit that having a utility power outage, for any 'extended' length of time, is very, very rare...so rare, in fact, that we rarely ever even 'plan' for it, since, well, the normal day-to-day life tends to help us rely on the basics that we have 24/7, without much thought, otherwise.
Tell me you don't live in Southeast Michigan without telling me you don't live in Southeast Michigan.

Next thing you'll say is roads are smooth, I bet.😂
 

Sponsored

chriserx

Well-known member
First Name
Chris
Joined
Oct 3, 2025
Threads
1
Messages
122
Reaction score
69
Location
Louisiana
Vehicles
2025 Ford Lightning Flash Job 2 😭
Have you tested it?
I have a similar setup but when we had a power outage, the truck would not allow the connection and would throw the breaker on the 30amp connection in the truck.
But when I hooked it up to generator the Generlink worked fine. Not sure why yet
Central AC would be the most likely candidate for this. If not that, the next thing I'd check would be a leg imbalance. It can power a total of 7200w but only 3600w per leg. Inverters will enforce this pretty strictly. Non inverter generators are more tolerant but not immune.

Edit: After reading all of the responses @flyct makes a good point about the ground, especially if it were immediate.
 
Last edited:

chl

Well-known member
First Name
CHRIS
Joined
Dec 16, 2022
Threads
7
Messages
2,178
Reaction score
1,340
Location
alexandria virginia
Vehicles
2023 F-150 LIGHTNING, 2012 Nissan Leaf, 2015 Toyota Prius, 2000 HD 883 Sportster
Occupation
Patent Atty / Electrical Engineer
Have you tested it?
I have a similar setup but when we had a power outage, the truck would not allow the connection and would throw the breaker on the 30amp connection in the truck.
But when I hooked it up to generator the Generlink worked fine. Not sure why yet
GFCI detected a ground fault.
If wired correctly through a neutral switching transfer switch (e.g., GENERAC 6853) I don't have that issue.
If you used a neutral switching transfer switch, then there may be a mis-wired neutral somewhere - I had that happen with one load neutral when I first tested mine - a lot of the load neutrals in the service panel were very close together so it was hard to figure out which was which.
 

chl

Well-known member
First Name
CHRIS
Joined
Dec 16, 2022
Threads
7
Messages
2,178
Reaction score
1,340
Location
alexandria virginia
Vehicles
2023 F-150 LIGHTNING, 2012 Nissan Leaf, 2015 Toyota Prius, 2000 HD 883 Sportster
Occupation
Patent Atty / Electrical Engineer
One quirk I forgot to mention with the GENRAC transfer switch used with the Lightning is if there is utility power available when you switch to or from the Lightning and the Lightning PPOB is enabled, it will trip the Lightning breaker due to an apparent small transient from the solenoid that actuates the switch.

Resetting the Lightning breaker clears the trip.

I and some other GENERAC Lightning owners have noticed this when testing.

See video the very end here when he switches back to utility and shows the Lightning screen:



PS: no need to ignore the code and disconnect the ground from the source (Lightning) to the loads.