Request: A concise answer to how to connect Pro Power to a generator inlet

mekuhl

New member
Joined
May 9, 2023
Threads
1
Messages
3
Reaction score
2
Location
Texas
Vehicles
2023 F-150 Lightning Lariat ER
Searching through this forum about connecting Pro Power to a generator inlet results in many well informed extensive discussions, but I can't seem to find concise instructions. I see many mentions of dealing with neutral wires that often turn into debates on the merits of various approaches. I'm down for a good debate when I understand the subject area, but I'm at sea for this topic. Searching the web gets lots of generator inlet tutorials but nothing specific to Pro Power as far as I can find.

Reason I'm asking is that I'm having a generator inlet and interlock installed soon, but I don't know if I need to tell the electrician anything special about Pro Power or if I can let them do a typical installation and I just need to get a specific cable for Pro Power.
Sponsored

 

Henry Ford

Well-known member
First Name
John
Joined
Dec 21, 2022
Threads
4
Messages
627
Reaction score
883
Location
Michigan
Vehicles
2022 F150 Lightning
ProPower has GFCI protection which will trip if neutral touches ground at any point other than the frame of the truck. There's no getting around that fact.

If you plug ProPower into a power inlet box connected to a breaker with an interlock on your panel the GFCI will trip and you won't have power because every circuit in your house connects neutral to ground at the panel.

In order to use ProPower to power your house you need a solution that switches the neutrals of every circuit you want powered. There are various ways to go about this. I have yet to see a code compliant way to do this so I'll stop here.

I know you are looking for a quick answer but there really isn't one. I suggest reading threads about the Generac 6852 to educate yourself about the capabilities of ProPower, the options available, and the threats of using each option.
 
OP
OP

mekuhl

New member
Joined
May 9, 2023
Threads
1
Messages
3
Reaction score
2
Location
Texas
Vehicles
2023 F-150 Lightning Lariat ER
OK, after even more searching I might have found a concise answer:
Best would be to tell him you would like to put in a generator transfer switch, for a 10 kW generator with a bonded neutral, and a 14-30R receptacle to plug the generator into. Then whether you use the truck or an actual generator to power your house, you are all set.
Thoughts?
 
Last edited by a moderator:

Amps

Well-known member
Joined
Feb 21, 2022
Threads
5
Messages
1,293
Reaction score
1,418
Location
Mid-Atlantic
Vehicles
Bolt
Thoughts?
IMHO, you already got the best answer from @Henry Ford if you don't want to use extension cords directly from the truck. It may not be elegant, but it's not bad for areas with fairly reliable grids.
I suggest reading threads about the Generac 6852 to educate yourself about the capabilities of ProPower, the options available, and the threats of using each option.
 

carys98

Well-known member
First Name
Cary
Joined
Jan 15, 2022
Threads
19
Messages
433
Reaction score
633
Location
Raleigh, NC
Vehicles
2023 Lightning Lariat SR
Last edited by a moderator:

Sponsored

v2h8484

Well-known member
Joined
Mar 3, 2023
Threads
3
Messages
120
Reaction score
48
Location
USA
Vehicles
Tesla Model 3
Reason I'm asking is that I'm having a generator inlet and interlock installed soon, but I don't know if I need to tell the electrician anything special about Pro Power or if I can let them do a typical installation and I just need to get a specific cable for Pro Power.
Tell the electrician you need to connect a "separately derived system" generator in a way that is compliant with your local building codes and any permit/inspection requirements.
 

Box Cat

Active member
Joined
Feb 25, 2024
Threads
0
Messages
36
Reaction score
26
Location
Portland, OR
Vehicles
2023 F-150 Lightning Lariat ER
OK, after even more searching I might have found a concise answer:


Thoughts?
Not only you would have to tell the electrician that the generator is neutral bonded, but that it has GFCI.
 
Last edited by a moderator:

hturnerfamily

Well-known member
First Name
William
Joined
Jan 8, 2022
Threads
37
Messages
1,479
Reaction score
1,685
Location
rural Georgia
Vehicles
22 LIGHTNING PRO IcedBlueSilver 8/23/2022
Occupation
Owner
I simply use the same exact NEMA14-50 I normally use to charge... at least this is MY way of doing it, many may warn against it, but it works, and has several times I've needed it:

Ford F-150 Lightning Request: A concise answer to how to connect Pro Power to a generator inlet 1711309599907-da

 
Last edited:

TaxmanHog

Moderator
Moderator
First Name
Noel
Joined
Jan 19, 2022
Threads
154
Messages
10,393
Reaction score
10,630
Location
SE. Mass.
Vehicles
2022 Lightning Lariat-ER Max Tow
Occupation
Retired

Sponsored

Newton

Well-known member
Joined
May 27, 2021
Threads
5
Messages
173
Reaction score
225
Location
WA State
Vehicles
VW e-Golf, Lariat SR, Kia EV6, Toyota T-100
It should be no problem for a decent electrician. It is a separately derived system as v2h8484 said. You will need a three wire transfer switch like the Generac Homelink 30A ($379) and any circuits that you want backed up moved to it. It is no big deal but may cost a bit more time than you expect since it involves more fiddling around in your circuit panel than if you did not have to do it. Should not cost an arm and a leg, though.

If you are in Washington make sure that the electrician installs a label onto the inlet that says something like "WARNING FOR CONNECTION OF A SEPARATELY DERIVED (BONDED NEUTRAL) SYSTEM ONLY." They have gotten picky about that here.

If you have another generator you will have to follow the instructions to convert it to a bonded neutral system if you want to use it with that inlet.

Bonded vs unbonded neutrals are a pain, NEC really should have required different plugs for the two scenarios.

If you are in Canada then there are some extra complexities.
 

ctuan13

Well-known member
First Name
Chuck
Joined
Jul 31, 2022
Threads
21
Messages
527
Reaction score
639
Location
Pittsburgh, PA
Vehicles
1979 Continental, 2022 F150 Lightning, 03 Marauder
I simply use the same exact NEMA14-50 I normally use to charge... at least this is MY way of doing it, many may warn against it, but it works, and has several times I've needed it:

1711309599907-da.png

So wait just to clarify, you're back feeding power into the nema 14-50 receptacle you normally use to charge?
 

GoodSam

Well-known member
First Name
Good
Joined
Jan 5, 2022
Threads
29
Messages
476
Reaction score
238
Location
93111
Vehicles
17CRV, 22 Lightning XLT 312A SR iced blue silver
Occupation
occupying space
Backup power transfer meter manual:
https://www.pge.com/assets/pge/docs...er-transfer-meter-manual.pdf.coredownload.pdf

Max 30Amps or 7.2kW load (matches the pro power bed outlet 240Vac available) so one would need to drop excessive loads like hard start air conditioning, etc.
I would think solar systems would need to be dropped as well as the truck may not be able to take in power if fully charged.

Great way to go by saving much higher costs of a separate panel and wiring. Especially if PG&E will provide and install for free!
 

Pioneer74

Well-known member
Joined
Aug 16, 2021
Threads
29
Messages
3,173
Reaction score
5,440
Location
Dearborn
Vehicles
2022 Lightning Lariat ER - 2022 Mach-E Premium
Occupation
Electrician
While everyone who has posted is trying to provide good & safe info, please understand this is now obsolete information.

the new meter collars with generator input provide the functionality you want.
They are only an option if your utility has approved them.