beatle
- Jun 1, 2021
- Springfield, VA
- Model S, Ridgeline, Miata, motorcycle(s)
And my axe!...and his house
They didn’t mention any neutral issues in the video. Is the power boost setup different than the Lightning with respect to the ground fault tripping?I think this video has a similar set-up from Fast Lane Truck. Check it out, might help.
My thought was that the Lightning gfci tripped because the bonded neutral in the house panel allowed current to return through both the neutral and ground to the truck. That would cause the fault of more than 5mA. If the ground path is eliminated by having another independent ground rod dedicated to the truck (and the portable generator when it’s used instead) the gfci would be eliminated.I am a newby here and a retired electrician, maybe I can be some help.
The 240V AC outlet on your Lighting or Pro Power is there for a tool. Such as an air compressor.
Not to run your house.
The 240V has GFCI protection. The GFCI is NOT there to protect you or whatever you plug into it.
It is there to protect your Pro Power and all wiring in the truck.
A GFCI does not trip due to over current.
Removing any of the four conductors removes the GFCI protection and could cause great damage to your trucks system.
This is why Ford wants you to run your house off the charging cord and converter on house instead of truck. Making it very expensive.
That would be a much cheaper solution for me than having to install a transfer switch for the neutral.My thought was that the Lightning gfci tripped because the bonded neutral in the house panel allowed current to return through both the neutral and ground to the truck. That would cause the fault of more than 5mA. If the ground path is eliminated by having another independent ground rod dedicated to the truck (and the portable generator when it’s used instead) the gfci would be eliminated.
Do you think that prevents potential damage to the truck?
If the ground wire in the 4 prong plug in the Lightning is there to take stray current away from the the truck (and the gfci trips when power is returned to the truck through the ground line) an independent ground may work. I’d like to hear from an electrician about that.That would be a much cheaper solution for me than having to install a transfer switch for the neutral.
Good summary.I hope this helps.
If a 4ma to 6ma current flows from circuit to earth, the GFCI will trip regardless of where the nearest electrical grounded surface is.
The way a GFCI functions is that all of the circuit conductors pass through a single current transformer. Because of Kirchhoff's Current Law, any current flowing 'out' on one circuit conductor must be exactly balanced by current flowing 'in' on the other circuit conductor(s), unless some current is flowing someplace else (eg. a ground fault, or a fault to another circuit). The _net_ current seen by the GFCI is thus zero when the protected circuit is functioning properly. The 'sum of all currents' measurement is what the GFCI is looking at.
Grounding the truck ( not sure how that would be done) with a ground rod or other means you might be grounding two systems together that MIGHT be separate in the truck. IDK.
Because the truck sits on rubber tires the electric systems are already engineered to not need an earth ground.
You aren't! just a few weeks before the Lightning "reveal" I sold my 5 year old portable generator with the intent on replacing it with a newer, quieter, one. The Lightning annoucement saved me from buying a $1200 generator! I've now been patiently waiting for my order letter going 18 months without power protection but it will be worth the wait. I already have a transfer switch and a 20ft cable so I'm ready to plug in the Lightning when it arrives! (next spring?)You know what I hate. A) My loud, stupid generator B) Spending more money on Ford than I have to. So, if a simple solution exists, awesome!
You guys are awesome. Thank you.... Is anyone else doing this? I mean, I can't be the only one with a generator and a whole house feed that bought a Lightning.
The purpose of the ground wire from the truck is to cause the breaker (GFCI) to trip in case the tool (or whatever is plugged in) has an internal fault that would otherwise cause exposed metal parts to become “hot.”I’m waiting to hear back from my electrician about my question that Randy and Dave addressed. But what does the ground wire do for the truck if grounding isn’t needed? I think someone else tried bypassing the ground wire but I can’t find that thread.
I don’t want to be electrocuted and I don’t want to fry my truck.
My electrician came back with a quote for setting it up with the Generac transfer switch. ~$2,700, too rich for my blood for the few hours a year we lose power. Extension cords it is!I’m waiting to hear back from my electrician about my question that Randy and Dave addressed. But what does the ground wire do for the truck if grounding isn’t needed? I think someone else tried bypassing the ground wire but I can’t find that thread.