Sponsored

Whole home back up - a simple approach

Johnif

Member
First Name
John
Joined
Feb 5, 2024
Threads
1
Messages
12
Reaction score
10
Location
Reno, NV
Vehicles
MY x2, Lightning XLT ER 2023
Hi all,
I just successfully tested my new home back up based on F150 Lightning. Works great.

I have a previously installed 19kW PV Solar system, Solaredge Inverters with Backup Interface feeding a whole house main panel that handles all circuits, except EV charging.

I implemented a whole home back up connected to F150 Lightning, based on:
1) external 50A generator input port (ground wire not connected)
2) 40A breaker in main panel, with standard lockout device to main breaker
3) additional 125A subpanel, with 125A breaker used to switch Neutral line from utility side on/off.

Total material cost approx $200, and another $75 for 50A extension cable to the truck.

I realize it may not be as automated as the HIS system or a single transfer switch, but it allows me to back up my whole main panel without moving any circuits, and it is lower overall cost, and no dealing with Sunrun etc...

Ford F-150 Lightning Whole home back up - a simple approach 20240205_171250
Ford F-150 Lightning Whole home back up - a simple approach 20240205_181501
Ford F-150 Lightning Whole home back up - a simple approach 20240205_171235
Sponsored

 
Last edited:

Mmiketa

Well-known member
Joined
Nov 25, 2023
Threads
2
Messages
221
Reaction score
301
Location
Virginia, USA
Vehicles
'23 Lightning Lariat ER
Im not sure I’m following your whole setup, but you do not want to switch the house neutral AND remove the ground from the truck. You want one neutral-ground bond in your system and you want it to be at the service point ie the truck when in backup mode.
 
OP
OP

Johnif

Member
First Name
John
Joined
Feb 5, 2024
Threads
1
Messages
12
Reaction score
10
Location
Reno, NV
Vehicles
MY x2, Lightning XLT ER 2023
Im not sure I’m following your whole setup, but you do not want to switch the house neutral AND remove the ground from the truck. You want one neutral-ground bond in your system and you want it to be at the service point ie the truck when in backup mode.
Alright, good point, will look into this. Should be easy to apply
 

TaxmanHog

Moderator
Moderator
First Name
Noel
Joined
Jan 19, 2022
Threads
211
Messages
15,622
Reaction score
17,460
Location
SE. Mass.
Vehicles
2022 Lightning Lariat-ER & 2024 HD Road Glide CVO-ST
Occupation
Retired
?

This is not a recommended method of connection {dispensing with the ground between truck and generator input or input to main load center}.

There are other threads which deal with the safer way to implement a generator input to transfer switch that includes neutral switching.
 

Mmiketa

Well-known member
Joined
Nov 25, 2023
Threads
2
Messages
221
Reaction score
301
Location
Virginia, USA
Vehicles
'23 Lightning Lariat ER
?

This is not a recommended method of connection {dispensing with the ground between truck and generator input or input to main load center}.

There are other threads which deal with the safer way to implement a generator input to transfer switch that includes neutral switching.
For what it’s worth, I don’t think it’s unsafe to not bring over your equipment ground from the truck. You service doesn’t bring you a ground either, you make the ground at the house and then bond the neutral. Treat your car as the utility and it’s the same thing, and its built in ground loop will clear its faults. This method is not code legal though which is also important.
 

Sponsored
OP
OP

Johnif

Member
First Name
John
Joined
Feb 5, 2024
Threads
1
Messages
12
Reaction score
10
Location
Reno, NV
Vehicles
MY x2, Lightning XLT ER 2023
For what it’s worth, I don’t think it’s unsafe to not bring over your equipment ground from the truck. You service doesn’t bring you a ground either, you make the ground at the house and then bond the neutral. Treat your car as the utility and it’s the same thing, and its built in ground loop will clear its faults. This method is not code legal though which is also important.
Thanks guys. really appreciate your perspectives. I can implement either option, always good to stick with the rule book
 

Ford Motor Company

Well-known member
Official Ford Account
First Name
Brian
Joined
May 26, 2021
Threads
51
Messages
1,980
Reaction score
2,766
Location
Michigan
Vehicles
F-150 Lightning
Occupation
Real Human & Community Manager
Hi all,
I just successfully tested my new home back up based on F150 Lightning. Works great.

I have a previously installed 19kW PV Solar system, Solaredge Inverters with Backup Interface feeding a whole house main panel that handles all circuits, except EV charging.

I implemented a whole home back up connected to F150 Lightning, based on:
1) external 50A generator input port (ground wire not connected)
2) 40A breaker in main panel, with standard lockout device to main breaker
3) additional 125A subpanel, with 125A breaker used to switch Neutral line from utility side on/off.

Total material cost approx $200, and another $75 for 50A extension cable to the truck.

I realize it may not be as automated as the HIS system or a single transfer switch, but it allows me to back up my whole main panel without moving any circuits, and it is lower overall cost, and no dealing with Sunrun etc...

20240205_171250.jpg
20240205_181501.jpg
20240205_171235.jpg
That's great to hear, John! The intelligent backup power system of the F-150 Lightning is most certainly awesome, and a feature we're proud to offer!
 

Its PJ Bia

Well-known member
Joined
Jan 11, 2023
Threads
4
Messages
285
Reaction score
283
Location
Maine
Vehicles
F150 Lightning PRO
I've used this same setup to now power our house through several multi-day outages. I know its not to code, and if I were using this to power our house daily I would probably look at another solution, but this current setup allows me to power all 33 breakers I have in my 200amp panel which no transfer switch would allow me to do. It also cost me $0 because I already had the generator hookup installed for our gas generator.
 

Zprime29

Well-known member
First Name
Brandon
Joined
Jul 26, 2022
Threads
42
Messages
2,507
Reaction score
2,670
Location
Tucson, AZ
Vehicles
2022 Lightning ER, 2025 XC90 Recharge
That's great to hear, John! The intelligent backup power system of the F-150 Lightning is most certainly awesome, and a feature we're proud to offer!
I don't think you fully understand what's going on here.
 

Zprime29

Well-known member
First Name
Brandon
Joined
Jul 26, 2022
Threads
42
Messages
2,507
Reaction score
2,670
Location
Tucson, AZ
Vehicles
2022 Lightning ER, 2025 XC90 Recharge
Hi all,
I just successfully tested my new home back up based on F150 Lightning. Works great.

I have a previously installed 19kW PV Solar system, Solaredge Inverters with Backup Interface feeding a whole house main panel that handles all circuits, except EV charging.

I implemented a whole home back up connected to F150 Lightning, based on:
1) external 50A generator input port (ground wire not connected)
2) 40A breaker in main panel, with standard lockout device to main breaker
3) additional 125A subpanel, with 125A breaker used to switch Neutral line from utility side on/off.

Total material cost approx $200, and another $75 for 50A extension cable to the truck.

I realize it may not be as automated as the HIS system or a single transfer switch, but it allows me to back up my whole main panel without moving any circuits, and it is lower overall cost, and no dealing with Sunrun etc...
Does your solar still operate while using the Lightning as the backup source?
 
  • Like
Reactions: dww

Sponsored

v2h8484

Well-known member
Joined
Mar 3, 2023
Threads
3
Messages
214
Reaction score
110
Location
USA
Vehicles
Tesla Model 3
For what it’s worth, I don’t think it’s unsafe to not bring over your equipment ground from the truck. You service doesn’t bring you a ground either, you make the ground at the house and then bond the neutral. Treat your car as the utility and it’s the same thing, and its built in ground loop will clear its faults. This method is not code legal though which is also important.
Just FYI, the way most people are using the neutral transfer switch with the truck is also not code compliant per NEC Section 250.34(B) (https://up.codes/s/portable-and-vehicle-mounted-generators). The truck ground needs to be connected to its own ground rod to be code compliant.
 

Henry Ford

Well-known member
First Name
John
Joined
Dec 21, 2022
Threads
9
Messages
1,670
Reaction score
2,453
Location
Michigan
Vehicles
2022 F150 Lightning Platinum
Just FYI, the way most people are using the neutral transfer switch with the truck is also not code compliant per NEC Section 250.34(B) (https://up.codes/s/portable-and-vehicle-mounted-generators). The truck ground needs to be connected to its own ground rod to be code compliant.
Will you quote the section you are referring to? I can't find it and I don't understand how requiring a grounding rod on a vehicle makes sense.
 
  • Like
Reactions: GDN

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
4,161
Reaction score
5,509
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER

Zprime29

Well-known member
First Name
Brandon
Joined
Jul 26, 2022
Threads
42
Messages
2,507
Reaction score
2,670
Location
Tucson, AZ
Vehicles
2022 Lightning ER, 2025 XC90 Recharge
Yes, works fine. Have it all inverters wired through Backup Interface, managed separately from main panel.
Very cool. I've been interested in a way to use my solar while backing up power with the lightning. I believe I recall someone saying that excess solar was charging their truck while using the HIS and FCSP setup. Just not sure it's worth that price tag and potential headache.
Sponsored

 
 