I already have a GENERAC 6854 transfer switch installed for use with my '22 Powerboost - can I simply use the 240V output in the Lightning to power this panel? I'm considering getting a Lightning but not sure if I will have to add another configuration to power house. I also have a 30A receptacle to power my main panel which I have a 13000W tri fuel generator. I have soft starts on my 4 ton and 2 ton AC units, so AC's are not an issue.
Just real simple - is my GENERAC switch "PLUG n PLAY" with the LIGHTNING?
Sponsored

 

Runaway Tractor

Well-known member
Joined
Jan 25, 2024
Threads
14
Messages
639
Reaction score
1,048
Location
USA
Vehicles
Yes
6852 Sub Panel: Yes. No further action required.

Regarding the other inlet to the main panel, I assume you have that on a breaker interlocked with the main breaker. You can use the pro power on that too. However you'd have to disconnect the ground from the truck to avoid tripping the truck's GFCI (the reason most people get the 6852 subpanel instead). I have a 30 inlet with the ground disconnected (floating neutral input) with an interlock on the main so I can run the entire house.
 
OP
OP
Texdan

Texdan

Active member
First Name
Dan
Joined
Sep 4, 2025
Threads
4
Messages
28
Reaction score
51
Location
Magnolia, TX
Vehicles
'25 LIGHTNING PLATINUM , '23 INFINITY QX60, '07 DODGE MAGNUM SRT8
Occupation
self employed
6852 Sub Panel: Yes. No further action required.

Regarding the other inlet to the main panel, I assume you have that on a breaker interlocked with the main breaker. You can use the pro power on that too. However you'd have to disconnect the ground from the truck to avoid tripping the truck's GFCI (the reason most people get the 6852 subpanel instead). I have a 30 inlet with the ground disconnected (floating neutral input) with an interlock on the main so I can run the entire house.
Do you know if GENERAC 6854 and 6852 are similar? Please advise.
 

Sponsored
OP
OP
Texdan

Texdan

Active member
First Name
Dan
Joined
Sep 4, 2025
Threads
4
Messages
28
Reaction score
51
Location
Magnolia, TX
Vehicles
'25 LIGHTNING PLATINUM , '23 INFINITY QX60, '07 DODGE MAGNUM SRT8
Occupation
self employed
OK thanks guys - looks like the LIGHTNING will be "PLUG N PLAY" with my GENERAC 6854 set up -- much appreciated!
Now to get a deal on a LIGHTNING LARIAT! -
I am noticing several things about new LIGHTNING sales -
1. none listed on AUTOTRADER
2. Trims under LARIAT and PLATIMINUM do not (typically) come with the twin panel moonroof - I want one with a sunroof (moonroof).
 

CD4TNF

Well-known member
Joined
Jun 8, 2024
Threads
17
Messages
217
Reaction score
295
Location
PNW
Vehicles
2022 F150 Lightning Platinum
My go-to websites for car shopping are cars.com, carmax, carvana, edmunds, iseecars.com. Hope you find your deal.
 

RickLightning

Well-known member
Joined
Jan 17, 2022
Threads
93
Messages
6,051
Reaction score
8,154
Location
SE MI
Vehicles
'22 Lightning ER Lariat,'22 Mach-E Premium 4X
Make sure you buy a ProPower 9.6kW, not 2.4kW.
 
OP
OP
Texdan

Texdan

Active member
First Name
Dan
Joined
Sep 4, 2025
Threads
4
Messages
28
Reaction score
51
Location
Magnolia, TX
Vehicles
'25 LIGHTNING PLATINUM , '23 INFINITY QX60, '07 DODGE MAGNUM SRT8
Occupation
self employed
Make sure you buy a ProPower 9.6kW, not 2.4kW.
Yes thank you - did not know there are 2 options, but like the PB I have the 7.2Kw inverter. So will look for the 9.6 Kw.
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
4,036
Reaction score
5,267
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
Yes thank you - did not know there are 2 options, but like the PB I have the 7.2Kw inverter. So will look for the 9.6 Kw.
7.2 is the max used to power a house. 9.6 is the sum of the 7.2 powering the bed outlets and a separate 2.4 inverter (which is 120V only) that powers the cab and frunk outlets.
 

Sponsored

RickLightning

Well-known member
Joined
Jan 17, 2022
Threads
93
Messages
6,051
Reaction score
8,154
Location
SE MI
Vehicles
'22 Lightning ER Lariat,'22 Mach-E Premium 4X
Yes thank you - did not know there are 2 options, but like the PB I have the 7.2Kw inverter. So will look for the 9.6 Kw.
There have been numerous people that didn't, and bought, and then said "where is my 240v outlet"? I was at an EV meet this summer with one, proudly showing me his Flash, and saying "see my 240v outlet" but he didn't have one. The look on his face at the time wasn't pretty...

Of course there were a bunch of other features he thought had that he didn't, but he did no research, just went and bought it.
 

kstype

Well-known member
First Name
Kurt
Joined
Jul 21, 2023
Threads
11
Messages
268
Reaction score
343
Location
Pennsylvania
Vehicles
2023 F-150 Lightning Lariat ER
Occupation
Principle Systems Engineer
Hi,

I too have a generator port that I use with my 6.5 kw Generac portable generator with a manual service disconnect switch at my panel. I am able to use the 7.2KW pro power onboard using the same cable to power my house without any issues.

I just used this a couple months ago to power our home for about 24 hours continuously after some heavy storms rolls through SE Pennsylvania.

Unfortunately we had a neighbor with a gas generator that he kept too close to the house and it started a fire - and they are still trying to recover from that.

I was very happy to have the use of the quiet and zero exhaust ProPower onboard.
.
Ford F-150 Lightning Lightning powering house - IMG_4447


Ford F-150 Lightning Lightning powering house - IMG_0626
Ford F-150 Lightning Lightning powering house - IMG_0625


Ford F-150 Lightning Lightning powering house - IMG_0627
 

MaintGrl

Well-known member
First Name
Marsha
Joined
Dec 21, 2023
Threads
8
Messages
537
Reaction score
537
Location
El Sobrante, Ca
Vehicles
2023 XLT Lightning, Anti-Matter Blue SR (311a)
Occupation
Retired CWEA Grade 3 Maintenance Technician
OK thanks guys - looks like the LIGHTNING will be "PLUG N PLAY" with my GENERAC 6854 set up -- much appreciated!
Now to get a deal on a LIGHTNING LARIAT! -
I am noticing several things about new LIGHTNING sales -
1. none listed on AUTOTRADER
2. Trims under LARIAT and PLATIMINUM do not (typically) come with the twin panel moonroof - I want one with a sunroof (moonroof).
Hi Dan, welcome to the forum. lots of smart folks here that can help when issues arise, AND for just general info. I have an 2023 XLT, without a sun/moon roof.
There have been folks here that have had issues with their sun/moon roof leaking, so do a lil research, then make your decision. Welcome, again....
 
OP
OP
Texdan

Texdan

Active member
First Name
Dan
Joined
Sep 4, 2025
Threads
4
Messages
28
Reaction score
51
Location
Magnolia, TX
Vehicles
'25 LIGHTNING PLATINUM , '23 INFINITY QX60, '07 DODGE MAGNUM SRT8
Occupation
self employed
Hi,

I too have a generator port that I use with my 6.5 kw Generac portable generator with a manual service disconnect switch at my panel. I am able to use the 7.2KW pro power onboard using the same cable to power my house without any issues.

I just used this a couple months ago to power our home for about 24 hours continuously after some heavy storms rolls through SE Pennsylvania.

Unfortunately we had a neighbor with a gas generator that he kept too close to the house and it started a fire - and they are still trying to recover from that.

I was very happy to have the use of the quiet and zero exhaust ProPower onboard.
.
IMG_4447.webp


IMG_0626.webp
IMG_0625.webp


IMG_0627.webp
PB 7.2Kw has been awesome - used it 3x last year and with key circuits on the GENERAC 6854 powered 2 fridges, 1 freezer, 2 small offices, 2 Ton A/C for Master BR, and microwave - we have gas WH and gas heat, so no issues there. I also splurged to run the whole panel, with a tri fuel 13000W DUROMAX and installed ICM soft starts on both AC units, and we can run the whole house with that setup. I agree - the sound issue (quiet) with the F150 PB is awesome - ICE engine would kick in about once an hour for 5 minutes to recharge the INVERTER. The DUROMAX is about 65 decibels, and we would close the garage door (generator outside) to mitigate that noise.
 
Last edited:

chl

Well-known member
First Name
CHRIS
Joined
Dec 16, 2022
Threads
6
Messages
1,903
Reaction score
1,121
Location
alexandria virginia
Vehicles
2001 FORD RANGER, 2023 F-150 LIGHTNING
I already have a GENERAC 6854 transfer switch installed for use with my '22 Powerboost - can I simply use the 240V output in the Lightning to power this panel? I'm considering getting a Lightning but not sure if I will have to add another configuration to power house. I also have a 30A receptacle to power my main panel which I have a 13000W tri fuel generator. I have soft starts on my 4 ton and 2 ton AC units, so AC's are not an issue.
Just real simple - is my GENERAC switch "PLUG n PLAY" with the LIGHTNING?
Assuming it was wired correctly, yes no changes required.

One thing we have noticed (by we I mean folks who have used the GENERAC transfer switches with the Lightning) is that if there is utility power being supplied to the GENERAC via the panel 50A breaker when making the switch to or from the Lightning, the Lightning will detect a ground fault and cut off the output at the 240V outlet - seems to be a short spike on connection to the Lightning under that scenario.

You can see it at the end of this video:


It does not mean there is a wiring error, although a wiring error could cause a real ground fault, so it can be a bit disconcerting - caused me to double check all my wiring for any errors, like picking the wrong neutral to transfer.