Here's something I missed. Generators, as in the ones sitting in garages all over America, and even modern inverter generators are not up for this task. Over testing the past month I have discovered that the 9kW continuous/11kW peak inverter generator I've been using can only give 5.5kW continuous on ethanol blend gas in Tulsa at 800ft above sea level, with 100deg humid air intake
I've since had discussions with people more in tune with ICE small engine performance both in the automotive world and mobile equipment world. It seems this project is going to have to wait for EFI generators to be able to get the full running power rating anywhere in the US. Luckily most of the generator companies are coming out with these as we speak. So, more testing is needed.
****************This is a great PSA for engineers
Here's something I missed. Generators, as in the ones sitting in garages all over America, and even modern inverter generators are not up for this task. Over testing the past month I have discovered that the 9kW continuous/11kW peak inverter generator I've been using can only give 5.5kW continuous on ethanol blend gas in Tulsa at 800ft above sea level, with 100deg humid air intake
I've since had discussions with people more in tune with ICE small engine performance both in the automotive world and mobile equipment world. It seems this project is going to have to wait for EFI generators to be able to get the full running power rating anywhere in the US. Luckily most of the generator companies are coming out with these as we speak. So, more testing is needed.
I consulted with Grok-3 about the derating of a generator in Tulsa, OK on a 100'F day. Here is my question?:
If a carburated 9.0Kw continous-run-rated gasoline generator running on 10% ethanol gasoline is run in Tulsa, OK at 800ft above sea level, what the most Kw it can produce when the temperature is 100 degrees outside ?
ANSWER BY GROK-3:
To determine the maximum kW output of a 9.0 kW continuous-run-rated carbureted gasoline generator operating in Tulsa, OK, at 800 feet above sea level with 10% ethanol gasoline at an ambient temperature of 100°F (37.8°C), we need to account for derating due to altitude and temperature. Below is the step-by-step analysis:1. Understand Derating FactorsGenerator output is affected by environmental conditions like altitude and temperature due to reduced air density, which impacts combustion efficiency and cooling. Derating adjusts the generator’s rated output to reflect these conditions.
- Altitude Derating: At higher altitudes, lower air pressure reduces oxygen available for combustion, decreasing power output. For gasoline generators, the general guideline is a reduction of 2–3% per 1,000 feet above sea level.
- Temperature Derating: High temperatures reduce air density, further limiting combustion efficiency. Manufacturers typically guarantee full power up to 40°C (104°F), with derating of approximately 3% per 5°C above 40°C. Since 100°F (37.8°C) is below 40°C, temperature derating may not apply unless specified otherwise by the manufacturer.
- Ethanol Blend: 10% ethanol gasoline (E10) has slightly lower energy content than pure gasoline (about 3–5% less energy per unit volume), which may slightly reduce output or efficiency but is typically accounted for in the generator’s design. Specific derating for E10 is not well-documented in the sources, so we’ll assume minimal impact unless specified.
- Altitude derating factor: 800 / 1,000 = 0.8
- Output reduction: 0.8 × 3% = 2.4%
- Reduction due to altitude: 9.0 kW × 0.024 = 0.216 kW
- Maximum output: 9.0 kW − 0.216 kW = 8.784 kW
- Reduction due to E10: 8.784 kW × 0.03 = 0.263 kW
- Adjusted output: 8.784 kW − 0.263 kW = 8.521 kW
- Manufacturer Specifications: The exact derating factors depend on the generator’s make and model. Some manufacturers provide specific derating tables or high-altitude kits to adjust the carburetor for better performance.
- Carbureted Engine: Carbureted engines are more sensitive to altitude than fuel-injected ones, as they cannot automatically adjust the air-fuel mixture. A high-altitude kit could mitigate some loss but isn’t mentioned in the query.
- Continuous vs. Peak Rating: The 9.0 kW rating is for continuous operation, so peak output might be slightly higher (e.g., 10–11 kW), but derating applies similarly. The answer focuses on continuous output as specified.
Likely the generator wasn't properly rated to start with.