Please help with my home charger install

William Munny

Active member
First Name
William
Joined
Nov 27, 2024
Threads
2
Messages
27
Reaction score
25
Vehicles
23 Lightning Pro
I will be using a licensed electrician but have read / seen on internet many licensed electricians unfamiliar with ev chargers, so hoping for some info here.

I purchased the ChargePoint home flex. Ideally would like to charge as fast as possible hardwired with the charger in my garage, but there is a great distance between my panel and garage, probably about 75 feet….also I might not have the room in my panel for higher amps….

so I’m open to suggestions. Luckily for me I have numerous low cost / free chargers available so rarely charge at home anyway (currently on level 1 outlet), but with tax write off and discount purchase through utility I figured I’d get the home charger, plus maybe I will be able to precondition the vehicle now.

Pics attached.

thanks in advance

Ford F-150 Lightning Please help with my home charger install IMG_0292


Ford F-150 Lightning Please help with my home charger install IMG_0296


Ford F-150 Lightning Please help with my home charger install IMG_0291


Ford F-150 Lightning Please help with my home charger install IMG_0295
Sponsored

 

Athrun88

Well-known member
Joined
Sep 30, 2024
Threads
0
Messages
158
Reaction score
178
Location
Toronto, Ontario, Canada
Vehicles
2024 F150 Lightning Lariat ER Avalanche
I had the same situation as you when I got my Chargepoint Home Flex installed. Main panel maxed out and far from the garage where I wanted the EVSE mounted. My solution was to add a new 200A panel in the garage which fed the main 100A panel. The garage panel would feed the Home Flex with a 60A circuit giving me the full 48A capacity I wanted. I had the electrician rough in a 2nd circuit for a future EVSE but this solution worked out perfectly for me.

This ended up being slightly cheaper than upgrading the old panel to a larger 200A panel since he didn't need to run new wires from the new garage panel to the 100A panel. Otherwise, he would have had to run a higher gauge cable from the grid to the main panel, then run another wire back from the main panel to the garage.

When I pitched this idea to 3 different electricians, the first one was a flat no but was also a pretty sketchy guy. The other two said yes but their prices/labour costs were different. Ended up going with electrician 3 because he had good vibes and was open to discussions and options.

EDIT: Snap, did not realize he was already at 200A on the main panel.. Might have to look at consolidating/eliminating some circuits around the house and running a 60A circuit to the garage for the EVSE to free up a slot. Leaving the above up for anyone else that might find themselves in a situation like mine!
 
Last edited:

DoyouLightning

Active member
First Name
BK
Joined
Feb 16, 2025
Threads
2
Messages
34
Reaction score
33
Location
Charlotte NC
Vehicles
23' lariat ER
How large is your house? Your panel already looks pretty full? Unless you have an empty circuit on that panel you might need to install a sub panel just for your garage.

Also note your service to the panel is 200 amps depending on the charger and rate you go up to your close to 35-50% of the capacity. When I charge my truck it's 80amps on the Ford pro charger but always changing at night as not to interfere with other power consumption.
 

Henry Ford

Well-known member
First Name
John
Joined
Dec 21, 2022
Threads
8
Messages
1,528
Reaction score
2,210
Location
Michigan
Vehicles
2022 F150 Lightning Platinum
Talk to an electrician. I don't see anything in that panel that would prevent a 50A charger circuit. I'm assuming you can either add double breakers or some of the unlabeled breakers are free. An electrician will be able to answer these questions. An EV charger isn't a difficult install.
 

Sponsored

El Duderino

Well-known member
Joined
Mar 25, 2025
Threads
1
Messages
45
Reaction score
30
Vehicles
25' Flash
You can have more amperage breakers in your panel than your service is rated for. You don't use them all at once...
 

swtaylor89

Active member
First Name
Scott
Joined
Sep 10, 2022
Threads
2
Messages
28
Reaction score
28
Location
San Bernardino
Vehicles
22 Ford Lightning
Occupation
Business Owner
I will be using a licensed electrician but have read / seen on internet many licensed electricians unfamiliar with ev chargers, so hoping for some info here.

I purchased the ChargePoint home flex. Ideally would like to charge as fast as possible hardwired with the charger in my garage, but there is a great distance between my panel and garage, probably about 75 feet….also I might not have the room in my panel for higher amps….

so I’m open to suggestions. Luckily for me I have numerous low cost / free chargers available so rarely charge at home anyway (currently on level 1 outlet), but with tax write off and discount purchase through utility I figured I’d get the home charger, plus maybe I will be able to precondition the vehicle now.

Pics attached.

thanks in advance

IMG_0292.jpeg


IMG_0296.jpeg


IMG_0291.jpeg


IMG_0295.jpeg
Like some others have said, you have plenty of room in there as many of those 20's and 15's can be combined to add in a 60amp or 100amp if you chose to do so. Absolutely get multiple quotes and go with who you feel would best do what you want done at a reasonable price. I would also second what some others have said and instead of running the charger straight from that panel, adding a subpanel, especially if you're a good distance away is a really good idea for future expansion possibilities. Think a 220v outlet for a portable charger, welder, air compressor, etc. Or an additional EV charger, or just more outlets near where the sub is. A lot less work to do so.
 

Al_V

Well-known member
First Name
Allen
Joined
Dec 16, 2023
Threads
1
Messages
138
Reaction score
139
Location
Canton, Ohio
Vehicles
2023 F-150 Lightning Lariat ER
If all else fails, get rid of the 4 breakers for garage heat and garage receptacles, run a 100A feeder to a new garage subpanel. Power those 3 circuits and your EVSE from the subpanel.
This is the best approach, and will also leave you with more new open slots in your main panel.
 

LHR

Member
First Name
LORENZO
Joined
Jun 21, 2024
Threads
1
Messages
11
Reaction score
10
Location
ontario can
Vehicles
F150 LIGHTNING
Occupation
RETIRED
you also try a couple of MCBs or tandem breakers to free to a couple slots.
 

Sponsored

Danface

Well-known member
First Name
Dan
Joined
Sep 19, 2023
Threads
4
Messages
896
Reaction score
912
Location
Central Mass
Vehicles
2023 Lightning XLT
Don't forget, you can most likely open a space or two by doubling up existing circuits onto a single breaker. Of course, be careful to not put the high usage/voltage ones together. I ran about 75 feet of 100 copper wire to my 80 amp charger, no issues.
 

K6CCC

Well-known member
First Name
Jim
Joined
Sep 12, 2024
Threads
18
Messages
442
Reaction score
363
Location
Glendora, Calif.
Vehicles
2024 Lightning Flash ER in Antimatter Blue, 2017 Toyota Corolla (wife's car)
Occupation
Two Way radio systems
Note that he likely can not use tandem breakers to make space. That is a 40 position panel and NEC does not allow tandem breakers in 40 position panels. However as others have suggested, a single 240 volt feed to a sub panel is the garage and then move all the existing garage circuits to the new sub panel would be the solution.

Also, I notice that a bunch of your existing breakers are not labeled. Take the effort to determine what breaker feeds every single device, outlet, and switch. Document that so you don't have to guess when something goes wrong. Easiest way to do that is have one person walking around the house with a light or test indicator and another person at the panel. Have the two people talking over radios or phones and the person at the panel kills breakers one at a time until the person at that outlet (etc) says "That's it". Repeat for every device, outlet, and switch. The person at the panel will quickly get an idea what breaker feeds an area of the house so it's not like you will have to go through 40 breakers for every outlet.
 

K6CCC

Well-known member
First Name
Jim
Joined
Sep 12, 2024
Threads
18
Messages
442
Reaction score
363
Location
Glendora, Calif.
Vehicles
2024 Lightning Flash ER in Antimatter Blue, 2017 Toyota Corolla (wife's car)
Occupation
Two Way radio systems
Can you provide a code reference for that? I’ve never seen it.
A quick Google search said 384-15
And I was in error, it's 42 branch circuits (not 40).

I know that on my main breaker panel (42 positions), there is a part of the bussbar that needs to have a notch in order for tandem breakers to be inserted. That notch is present in smaller panels, but not in the large panels.
 

bryansocko

Active member
First Name
Bryan
Joined
Feb 11, 2025
Threads
5
Messages
29
Reaction score
35
Vehicles
2023 Lightning Platinum
Sparky here. Have the electrician run 1/0 aluminum ser to the garage. Put in on a 125 amp breaker (this is the largest breaker you can get amperage wise that is a normal size that will fit in that panel) then install a 125 amp mlo panel on the garage. Yank out all the garage circuits from the main pain and place them in the garage panel. Now you will have a few extra spaces in the main panel and have plenty of headroom for growth in the garage panel.