House back up with 50amp RV outlet

Status
Not open for further replies.
First Name
Lance
Joined
Aug 7, 2025
Threads
4
Messages
20
Reaction score
53
Vehicles
2025 Lightning
So my Lightning charger plugs into a 50 amp 4 prong RV outlet in my garage. Couldn't I install a breaker interlock for the houses main breaker, and make a double ended male cable to go from the 30 amp end from the Lightning bed to the 50amp RV outlet in my garage, and backfeed my house that way? Seems overly simple? What am I missing?
Sponsored

 

TaxmanHog

Moderator
Moderator
First Name
Noel
Joined
Jan 19, 2022
Threads
206
Messages
15,129
Reaction score
16,762
Location
SE. Mass.
Vehicles
2022 Lightning Lariat-ER & 2024 HD Road Glide CVO-ST
Occupation
Retired
So my Lightning charger plugs into a 50 amp 4 prong RV outlet in my garage. Couldn't I install a breaker interlock for the houses main breaker, and make a double ended male cable to go from the 30 amp end from the Lightning bed to the 50amp RV outlet in my garage, and backfeed my house that way? Seems overly simple? What am I missing?
Suicide patch cords are highly frowned upon per NEC & Local Code, NO you shouldn't!!
 
OP
OP
pirate4x4lance
First Name
Lance
Joined
Aug 7, 2025
Threads
4
Messages
20
Reaction score
53
Vehicles
2025 Lightning
Suicide patch cords are highly frowned upon per NEC & Local Code, NO you shouldn't!!
I didn't ask if it was frowned upon, I'm not dumb enough to put the male end in my mouth while it's hot, I asked if it would work with the Lightning.
 

Sponsored

RLXXI

Well-known member
Joined
Jun 10, 2021
Threads
19
Messages
690
Reaction score
496
Location
S. E. Louisiana
Vehicles
2025 F 150 Flash, 2013 F 150 XLT, 2014 Escape, 2011 Suzuki DR 650SE
Occupation
Auto tech
So my Lightning charger plugs into a 50 amp 4 prong RV outlet in my garage. Couldn't I install a breaker interlock for the houses main breaker, and make a double ended male cable to go from the 30 amp end from the Lightning bed to the 50amp RV outlet in my garage, and backfeed my house that way? Seems overly simple? What am I missing?
Sure you can. Just remember to shut off the main breaker before you connect the truck.
 

potato

Well-known member
First Name
John
Joined
Feb 1, 2024
Threads
0
Messages
416
Reaction score
603
Location
BC, Canada
Vehicles
2023 F150 Lightning XLT ER
The truck will detect the neutral-ground bond at the panel as a ground fault and will not supply current. You could maybe leave the ground disconnected on your suicide cable, I don't know, but do two wrongs make a right?
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
4,036
Reaction score
5,267
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
With a breaker interlock as you describe, you’ll never be able to charge….the only time the outlet breaker can be on is if the main is off.
In addition to what everybody else is telling you.
 

Runaway Tractor

Well-known member
Joined
Jan 25, 2024
Threads
14
Messages
639
Reaction score
1,048
Location
USA
Vehicles
Yes
With a breaker interlock as you describe, you’ll never be able to charge….the only time the outlet breaker can be on is if the main is off.
In addition to what everybody else is telling you.
This is the dot that wasn't connecting (literally) on this plan. The interlock only allows one of the two breakers to be on at a time. Either the main or the generator (charger) outlet. Therefore you could not actually use the interlock.

Lots of people use a double-male death cable to connect a generator to an old existing 240v outlet, usually for a welder or clothes dryer. Those same people are doing this without an interlock on their panel main breaker. They do this by memory, remembering to make sure the main is off, and no touching energized prongs. So yes you CAN do this and it will work.

That said, I highly recommend against this tactic. The change of accidentally energizing I recommend pulling 10/3 to the garage for a proper generator inlet box, and put a new 30 amp breaker in the proper location adjacent to the main for the interlok. This is inexpensive in the grand scheme of electrical work. This may be easier said than done if your panel is on the other side of a finished basement or something. I had to run mine outside.